Addressing modes for output module in control logix 5000

kbn_120184

Member
Join Date
Aug 2012
Location
usa
Posts
85
Hi
i am converting plc5 program to control logix 5000 can any one suggest me how to do address output module .as we use bits in plc5 and words in control logix . And what else problem we can face while upgrading plc 5 to control logix 5000 .
Thank u
 
There is a good Rockwell Automation Reference Manual that describes the conversion of PLC-5 projects to ControlLogix, focusing on the Conversion Utility that comes with RSLogix 5000.

http://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1756-rm085_-en-p.pdf

The exact conversion of the original I/O address to your new system depends on the connection method of the original I/O (local, extended local, RIO, ControlNet) and whether you have migrated to a new network or a new platform for the new system.
 
The are addresed according to there rack position and some other info as follows:
Local:<RackSlotNo.>:I.data.<IO no.> - input
Local:<RackSlotNo.>:O.data.<IO No> - output
 

Similar Topics

Hi All, I am looking at a future project that includes a PLC5 with some digital I/O. Its been a long time since I have worked on the PLC5...
Replies
4
Views
1,584
I am very new to Modbus and the industry, so forgive me if I am missing something obvious. I have known Modbus register addresses coming from a...
Replies
7
Views
209
I have a system using Rx3I CRU320 redundant CPU with Proficy Machine Edition Software. In the hardware configuration of each CPU module, under...
Replies
14
Views
375
See the screenshot of EIP tag list. We are trying to read in a digital input that is hard-wired. It is shown here as I31.1. I believe we cannot...
Replies
7
Views
272
Hello all. I have a Simatic SM374 (374-sxh01-0aa0) sim module. I am using TIA portal v.18. I can't find this module in my list of hardware devices...
Replies
12
Views
742
Back
Top Bottom