Can't connect to Digi IAP any ideas?

Oh my god it's working!!
I changed from Allen Bradley Ethernet to Ethernet/IP on the Digi IAP Network Masters Protocol and rebooted the IAP....
Now to make a configuration backup...

Thanks again Okie for help and encouragement, it was greatly appreciated
 