Old August 7th, 2019, 11:54 PM   #1
ste1070
Member
Canada

ste1070 is offline
 
Join Date: Mar 2016
Location: Vancouver
Posts: 7
AB 1769-L18ERM-BB1B Embedded IO

Hi, I have a compact logix processor with embedded IO but the IO is not responding nor flashing on the self test when boots up. The IO light is just flashing and it does not see the IO in project. Any thoughts? Thanks
  Reply With Quote
Old August 8th, 2019, 06:19 AM   #2
jstolaruk
Lifetime Supporting Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,808
Share the project, may be something in the configuration.
__________________
I don't always test my code but when I do, I do it in production.
  Reply With Quote
Old August 8th, 2019, 10:13 AM   #3
ste1070
Member
Canada

ste1070 is offline
 
Join Date: Mar 2016
Location: Vancouver
Posts: 7
Sure but even creating a blank project doesn't seem to help. I'm guessing cause of catalogue number embedded IO should automatically be set up and it does appear in the tag database.

Ill sort a copy of project out and post. Thanks for your reply
  Reply With Quote
Old August 8th, 2019, 10:25 AM   #4
ste1070
Member
Canada

ste1070 is offline
 
Join Date: Mar 2016
Location: Vancouver
Posts: 7
here you go
Attached Files
File Type: zip test.zip (253.3 KB, 6 views)
  Reply With Quote
Old August 8th, 2019, 10:27 AM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 17,101
My recollection is that the embedded modules do flash their channel indicator LEDs during startup, so if yours don't do that and are showing a faulted connection to the controller, I would say that they are defective out-of-the-box.

Do you have any expansion I/O modules connected to the POINTBus ? Do those work ?
  Reply With Quote
Old August 8th, 2019, 10:39 AM   #6
jstolaruk
Lifetime Supporting Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,808
I'm trying to recall if on the face of the PLC there are two power inputs. One would be for processor power and one is for I/O power. If so, then both may need to be powered.
__________________
I don't always test my code but when I do, I do it in production.
  Reply With Quote
Old August 8th, 2019, 10:46 AM   #7
ste1070
Member
Canada

ste1070 is offline
 
Join Date: Mar 2016
Location: Vancouver
Posts: 7
Yes, I have both the processor and field power connected. Processor will run but IO light flashing.
  Reply With Quote
Old August 8th, 2019, 11:33 AM   #8
mike3475
Member
United States

mike3475 is offline
 
Join Date: Feb 2013
Location: brooklyn ,NY
Posts: 285
maybe you forgot the end cap.

https://rockwellautomation.custhelp....ype-03-code-23
  Reply With Quote
Old August 8th, 2019, 04:28 PM   #9
ste1070
Member
Canada

ste1070 is offline
 
Join Date: Mar 2016
Location: Vancouver
Posts: 7
this model doesn't need end cap as uses 1734 point IO type modules.
  Reply With Quote
Old August 8th, 2019, 06:32 PM   #10
jholm90
Member
Canada

jholm90 is offline
 
Join Date: Mar 2012
Location: Ontario
Posts: 133
Yep there's troubles afoot because I booted up my l16 yesterday and all the controller hardware IO flashes in sequence before point io expansion cards.

Try to reflash the firmware and verify expansion IO cards on 1st page of controller properties is set to correct number of installed point IO cards
  Reply With Quote
Old May 25th, 2023, 01:54 PM   #11
JCreel
Member
United States

JCreel is offline
 
Join Date: Apr 2020
Location: Mississippi
Posts: 46
I know this is an old thread, but i came across the same issue with a 1769-L18ERM-BB1b. I found out that you have to set the proper expansion modules in the controller properties. The default is 8 from a blank project, so if you are not using any additional modules, then it has to be set to 0. Then the IO will no longer claim that its faulted.

Hope this is useful.
__________________
**********
JCreel
**********

"Do or Do not, There is No Try" - Yoda
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB: forced read of IO Agrue LIVE PLC Questions And Answers 5 November 7th, 2018 04:34 PM
AB PLC5 to Contrologix, Keeping Existing IO harryting LIVE PLC Questions And Answers 5 January 16th, 2006 09:37 AM
AB 1794 Flex IO DaveW LIVE PLC Questions And Answers 4 January 6th, 2006 07:34 PM
AB Micrologix IO Addressing RichardB LIVE PLC Questions And Answers 13 April 12th, 2005 08:38 AM
AB PLC5/80B RIO Flex IO Fault corkers LIVE PLC Questions And Answers 9 September 4th, 2004 02:12 AM


All times are GMT -4. The time now is 08:06 AM.


.