Verify that LED indication light is working

Hi,
We are thinking of implementing a light to our safety system that indicates that a machine is in a ceratian more dangerous state then normal.

Talking to a safety specialist he said (but didn't know how to) that maybe I could have an indication if the light was broken. For example a relay is activated when the indication light is broken.

I can't figure out how to achieve this. Also I don't know HOW the indication light behave if it's broken. Does it still have the same internal resistance? Is it lower, higher or zero. It seems that he took this out of thin air without knowing there is a solution for it.

/Tim
  Reply With Quote
Old May 24th, 2023, 03:44 PM   #2
L D[AR2,P#0.0]
Lifetime Supporting Member
United Kingdom

L D[AR2,P#0.0] is offline
 
Join Date: Nov 2006
Location: UK
Posts: 6,537
Make it so the led is on when it is not more dangerous, if the LED fails then it indicates a more dangerous state than normal. Make it an illuminated pushbutton so you press it to test the LED.
__________________
S7-300 to 1500 conversions done - email (minus the spam) to spams7conversions@hotmail.com
  Reply With Quote
Old May 24th, 2023, 03:47 PM   #3
rQx
Lifetime Supporting Member
Sweden

rQx is offline
 
Join Date: Oct 2010
Location: Trelleborg
Posts: 1,008
Quote:
Originally Posted by L D[AR2,P#0.0] View Post
Make it so the led is on when it is not more dangerous, if the LED fails then it indicates a more dangerous state than normal. Make it an illuminated pushbutton so you press it to test the LED.
I would say that the "norm" is to have my flashing light indicate a more dangerous state. A non-lit light is not a good way to inform of a more dangerous state in my opinion since it does not catch the eye or make you aware that something is as it shouldn't be.

I could have two light, but then I would depend on that the faulty light is fixed before the other fails

/Tim
  Reply With Quote
Old May 24th, 2023, 04:06 PM   #4
tarik1978
Member
Morocco

tarik1978 is offline
 
Join Date: Mar 2010
Location: casablanca
Posts: 640
You can try a lamp failure detection like this one:
https://www.tele-online.com/en/case-...shy-detection/
__________________
Optimist will tell you the glass is half-full; the pessimist, half-empty; and the engineer will tell you the
glass is twice the size it needs to be
  Reply With Quote
Old May 24th, 2023, 05:06 PM   #5
ndzied1
Lifetime Supporting Member
United States

ndzied1 is offline
 
ndzied1's Avatar
 
Join Date: Aug 2002
Location: Chicago, Illinois
Posts: 2,795
Perhaps an acceptable approach would be to have redundant LED lights and include a testing feature. Then have instructions that an operator or maintenance person must verify the operation of the lights periodically.

I have also seen a lot of safety circuits specify that they be supplied by SIL rated power supplies and include a specific overcurrent rated device.
__________________
nOrM
======================
nOrM=Norman Dziedzic Jr.
I've never been to China but my phone has.
  Reply With Quote
Old May 25th, 2023, 03:25 AM   #6
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 2,451
The traffic light people already solved this by monitoring the current going to the lamp. That's one way of doing it, though if it's an LED it will be tricky I think.
  Reply With Quote
Old May 25th, 2023, 04:05 AM   #7
rQx
Lifetime Supporting Member
Sweden

rQx is offline
 
Join Date: Oct 2010
Location: Trelleborg
Posts: 1,008
Thanks!
I now have two approaches.
I found a relay from Schneider Electric RM35JA31MW that was an under/overcurrent relay, seems to fit my need. Also the redundant lights are an option
/Tim
  Reply With Quote
Old May 25th, 2023, 06:09 AM   #8
Puddle
Member
United Kingdom

Puddle is offline
 
Join Date: Mar 2022
Location: UK - The Norf
Posts: 169
I've heard of applications before where LED indicators were specified to have transistor feedback to show they were energised. I wonder if a faulty LED would be detected on the dark test from the failsafe IO though?
  Reply With Quote
Old May 25th, 2023, 11:17 AM   #9
widelto
Member
Colombia

widelto is offline
 
widelto's Avatar
 
Join Date: Jul 2005
Location: Barranquilla, Colombia
Posts: 3,305
I recall having seen many years ago a special output board that had a resistance and that resistance was used to measure if the light (bulb o led) at the end was ok or not. That was on Allen Bradley.
__________________
My two cents.
  Reply With Quote
Old May 25th, 2023, 07:02 PM   #10
TWS
Member
United States

TWS is offline
 
Join Date: Nov 2007
Location: virginia
Posts: 393
Preliminary Publication 1756-UM058D-EN-P - October 2004, Page 4-23 describes no load detection on diagnostic output modules.

1756-OA8D
1756-OB16D.
  Reply With Quote
Old May 25th, 2023, 08:16 PM   #11
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Nashville, Tennessee area
Posts: 3,493
we use AB safety gate locks and use the LOTO method.
the gate lock cannot be closed when a lock is on and the machine safety logic will not allow the machine to run without the gate lock being reset.
Can you do something like that?
james
  Reply With Quote
Old May 25th, 2023, 09:36 PM   #12
jholm90
Member
Canada

jholm90 is offline
 
Join Date: Mar 2012
Location: Ontario
Posts: 133
Please take a moment and look into muting lamps as they describe the concern noted. 1734-IB8S point-io input modules can have a "test output" (normally used for wiring in the estops) programmed as a muting output with current monitoring

https://literature.rockwellautomatio...t057_-en-p.pdf
  Reply With Quote
Old May 26th, 2023, 05:59 AM   #13
rQx
Lifetime Supporting Member
Sweden

rQx is offline
 
Join Date: Oct 2010
Location: Trelleborg
Posts: 1,008
The lamp and lower safety level is achieved with a key switch and a contactor relay (rated PLc).

In this safety level the machine can run with the lids open but only at 15% speed, this is what I want to indicate. As soon as the key switch is turned the light will flash indicating that IF the lids are open the machine can still turn at 15% speed. So I can't use any locks.

I appreciate the output modules examples but we use Siemens and the safety functions doesn't go through a PLC.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
How to control LED RGB light through PLC? Serhioromano LIVE PLC Questions And Answers 8 April 28th, 2016 01:29 AM
Siemens S5-95U issues, been working for years and now stop light lit BigTom209 LIVE PLC Questions And Answers 9 July 1st, 2011 04:26 PM
Light Beacon Not Working studentplc1 LIVE PLC Questions And Answers 11 March 8th, 2010 08:03 AM
O.T humour How many posters does it take to change a lightbulb. allscott LIVE PLC Questions And Answers 36 July 30th, 2008 01:58 PM
Any ideas about "testing" an LED? BJR LIVE PLC Questions And Answers 23 June 15th, 2005 08:48 AM


All times are GMT -4. The time now is 11:57 PM.


.