Sina_Pos problems
Holmux
Oct 2013
Aalborg
279
Dear All
I have a project with an Siemens S200 CPU controlling 2 S110 Serverdrives
I am using the Sina_Pos telegram and have everything working except the Absolute positioning using mode 2, I have tried everything I can think of but it will not fire.
Right now I have the Mode: 3, 5 and 7 working, but can't seem to get the mode 1 and 2 firering.
Any good advice ?
/Holmux
For an absolute move , your axis needs to be homed.
You sure you did that?
Do you get an error?
I don't see your velocity setpoint on the screenshot..looks like a 0
Hi JRW
Thanks for your reply.
In the screen shot the velocity is zero, my mistake I have tried all combinations I could think of.
I have mode a Homing true the mode 7, and it works well.
My actual position is 0 and I need to go down to position -4000 and back up to 0
If I have understood the manual correct, the drive will take the shortest way to the position and I don't need to set the direction, but what do i do the with velocity, do I set that to Minus ? or positive whit negative direction ?
/Holmux
If I go to mode 2 (with axis homed)
For homing- I just did a mode 5 - set reference point... then ExecuteMode bit
Now I can do an absolute move to -4000 using mode 2
Don't forget to toggle the ExecuteMode bit
There was some older test code in another program block, that was trying to shift to mode 5.
Once I got that cleared everything was working great.
I had another challenge, when I go to my minus position the unit is pressing against a plane with some spring tension for about 1 second, before I return to 0 position, when I used relative mode I never got the Position OK bit, bot when using mode 2 it works.
I never really got the full understanding of the Fly bit and when to use it, do you have a hint?
/Holmux
I have a machine which is undergoing upgradation. As part of the process two SEW drives are being replaced., existing Gen B with new Gen C. The...
197
Hello, I'm trying to test Acopos multi using Automation Studio. Ready LED is green blinking, how can i know what error of Acopos on Automation...
131
Hello all, i am new to the servo drive and this brand also. i installed the automation studio v4.12. i have to configure drive with plc B and R...
367
hi goodday to all, i have acopos 1320 as below title my acopos not driven a servo motor,. please help me,.
442
Hello, Does anybody have experience with ACOPOS drives? One of the machines at my plant uses B&R system with three ACOPOS 1016 drives. All three...
1,445