First time trying this particular combo. ML1400 and PLC5 over radio.
Initially I used 2 PLC5's and set them up to talk across the radio link and that worked just fine. So that clears the radio config from the equation
I set up MSG in the ML1400
This Controller:
Channel 2
PLC5 Read
N7:100
10 elements
Target Device:
timeout 5
N7:200
Node addr 35 (dec)
Local
2 errors depending on Channel protocol selection
Channel 2 set for DF1 Radio Modem:
Errors with message timed out in local processor
Channel 2 set for DF1 Full Duplex:
Error Hex 7 Target Node does not respond DF1 DLE Ack/NAK timeout . . .
ON difference I can see from the PLC5 and the ML1400 are
Channel in PLC5 is System Point to Point
There is no "typed" read in the ML1400
what am I not getting right here? Is DF1 Full Duplex right when radio is Simplex? (one freq for TX and RX)
Double-check the PLC-5 serial port error checking mode. The PLC-5 uses 1-byte BCC by default, while the MicroLogix uses 2-byte CRC by default.
To my knowledge the PLC-5 does not support the "DF1 Radio Modem" variant, so stick with DF1 Full Duplex.
Whether or not DF1 Full Duplex will work depends on how fast the radios turn around and how fast the "slave" device answers.
Hi Ken
Checked error correction, set both to CRC and also tried both to BCC. Still failed.
Slave device . . . meaning the PLC5 or the other radio?
Foung this on KB
.Must be a null modem cable between the 25 pin PLC5 serial port and the Micrologix serial port.
.Could use the 9 pin or mini round din on Micrologix side.
.The baud rates must match along with the error checking and you must change the node number on the Micrologix to 0. Don't use the default or the message will not work.
Didn't know about the node number being zero. this precludes having multiple PLCs on the same radio network...
I think the quick and dirty fix is to slap another 1400 near the PLC5 with one serial port on the radio network using DF1 radio protocol, and use its other serial port to talk to the PLC5.
If there is really a problem with this I'll replace the PLC with something better suited to comms. This location will be a master radio poll. I'm just testing the waters now.
A "null modem" cable is appropriate if there are is only wire between the two serial ports.
Because of the pinout differences between DB25 -> DB9, this is generally 2-2. 3-3, 7-5.
If you have radio modems in between the two controllers, then you connect them in the appropriate way to the radio modems.
The DB9 port is Port 2, and the round Mini-DIN port is Port 0. Make sure you are connected to the correct one.
This is if the MicroLogix is the originator of the message, and you are using DF1 Full Duplex.
If you are using DF1 Half Duplex, the configuration changes.
You mentioned only having one PLC on each side of the link, which is why I advised about DF1 Full Duplex.
The Duplex is the only area in question.
To my understanding of Police (or voice) radio , Full Duplex comms takes 2 frequencies, TX and RX so that both ends can talk at the same time or so the data or voice can the be repeated across hilltops.
That's not how my current system or this new one is configured. So I'm thinking that must not be what full duplex means as it pertains to this setting.
Master and Slave are the only half duplex options. So if I choose that option , with multiple hilltops covering the area I will still have multiple masters talking to the slave radios in their area.
I need a better understanding of this.
Most modern day serial radios will operate full duplex at least that's how it appears to the attached equipment (in this case the PLC's). They use transceivers that will switch from transmitting to receiving at such a high frequency rate the serial protocol never sees anything but a full duplex path.
What radios are you using?
That's kinda a broad brush (MDS makes/made a lot of radios) however given that it worked when it was both PLC5's it's probably not a half/full duplex thing. I would first connect the PLC's to each other without the radios and make sure that the protocol settings and port setting are all correct. Once you've got that working then put the radios in place. Keep in mind that cabling between the PLC's without the radios and with the radios will be different. Your best bet is to get a pinout of each devices serial port and make sure that you are going from the TX (transmit) pin of one device to the RX (receive) pin of the other (ground goes to ground). It's also worth noting that the TX and RX pins on a DB25 connector are the opposite than they are on a DB9 so a "straight through" cable will swap pins 2 and 3. A "Null" 25 to 9 cable will have pin 2 going to pin 2 and 3 to 3.
From everything I've read on this post I'm guessing you're having a cabling issue probably on the MicroLogix side.
Sorry - Radio is a GE MDS MCR Ethernet/Serial radio
I think we found the problem, but I'm setting up some more testing at the moment so we can drive around the area testing coverage.
These are set up as Access Point and Remote. Multiple remotes shortly.
Seems the Remote was missing the Access points IP address. Guess that wasnt written to NVram before unplugging.
I have them, both on the bench now and they are talking. Still not convinced.
A further caveat discovered... the MSG in the PLC will complete (DN bit set) as if its is satisfied, yet no data was transmitted (or read depending) to the other PLC . Its like the Radio satisfies the PLC before actually completing its job. That has not helped.
Update - Have GE Support on the phone with a sniffer in the traffic and a modbus simulator on both sides - appears that these radios are dropping part of message for no good reason.
Possibly unrelated: Using the L61 and BCC will cause the sniffer to show an error that the destination address data from the slave back to the master is empty. CRC doesnt do that - messages complete with either mode from the perspective of the PLC ladder.
Perhaps that BCC error is the equivalent of the missing data that GE support is noticing. Or it just clips the message too soon.
Interesting times.
Why are they using a Modbus simulator? Modbus RTU and DF1 are very different and will behave very differently across radios (with DF1 being much more forgiving). Unless the radio was specifically setup to deal with Modbus RTU it will drop packets. Having said that if the radios are setup to deal with Modbus RTU, DF1 will not be happy.
As to error checking, I have found in the past the BCC error checking does not work well on a wireless network. I would use CRC.
Modbus Exactly, we didn't want forgiving, we wanted solid.
We wound up clearing the radio, re-setting all the configs, set the Mcast Address from 254.100.0.5 to 254.0.0.0 (on request from support... not sure about that .0 address...)
Modbus started working properly, Moved back to the DF1 without changing the radio at all and comms worked properly.
Must have been a bad bit in the config from a solar flare. No definitive cause...
Now we create a hop (Remote -> AP -> Remote) and see if it will traverse it. Film at 11.
But I will say that the books and the tutorial videos for this model are both wrong in many places. The instructions work for the NX series - but not this model.
I need to read one analog tag located in a PLC5/40C 1.5 that has an ethernet card installed. I need to do this over ethernet to a Micrologix 1400...
2,103
Hi All. I can write an N7 value to a modbus register in an Automation Direct Servo but I can't read a holding register to an N7 address. I've...
1,919
Stuck at home and need to adjust the CVH on a PID loop. I can build an AdvancedHMI HMI to read write the valeus, but I cannot VPN in. Is there...
1,682
Hiii. i am trying to read the PLC-5/40c data to the ML1400 PLC throgh channel 0(25 pin to 9 pin pin configuration). When i downloaded the program...
17
5,080
Hi , in my application i was supposed to read the recipe name in a string & have to display it all other screens of scada & to perform operation...
2,909