I kinda have a weird issue with my factorytalk HMI. Here's the situation:
I have 2 operator stations running FT HMI side by side each with their own CPU.
Both .SED files should be the same.
We have a pump that pumps down a tank at a certain level
The pump has an indicator that monitors the amp draw
The pump auto shuts off at 10 inches
The alarm set points for the pump when running is Low at 6.8 and high at 9.8
When the pump shuts off at 10 inches, the program has a MOV instruction to auto set the low amp alarm to -10 so that it isn't in alarm when off.
Our alarm is set up to where it will blink red on the indication that is in alarm. Even if it goes out of alarm, it will continue to flash grey until the operator acknowledges the alarm
When the pumps shuts off, one operator station alarms at low amps even though it is out of alarm. It also shows up in the alarm history
The other operator HMI doesn't do this. It doesn't alarm or show up in the alarm history which is what we want bc the pump is shutting off normally.
Both alarms are setup the same as far as I can tell
Any ideas? Why would one station see an alarm but not the other? They are both look at the same controller.
I kinda have a weird issue with my factorytalk HMI. Here's the situation:
I have 2 operator stations running FT HMI side by side each with their own CPU.
Both .SED files should be the same.
We have a pump that pumps down a tank at a certain level
The pump has an indicator that monitors the amp draw
The pump auto shuts off at 10 inches
The alarm set points for the pump when running is Low at 6.8 and high at 9.8
When the pump shuts off at 10 inches, the program has a MOV instruction to auto set the low amp alarm to -10 so that it isn't in alarm when off.
Our alarm is set up to where it will blink red on the indication that is in alarm. Even if it goes out of alarm, it will continue to flash grey until the operator acknowledges the alarm
When the pumps shuts off, one operator station alarms at low amps even though it is out of alarm. It also shows up in the alarm history
The other operator HMI doesn't do this. It doesn't alarm or show up in the alarm history which is what we want bc the pump is shutting off normally.
Both alarms are setup the same as far as I can tell
Any ideas? Why would one station see an alarm but not the other? They are both look at the same controller.