Allen Bradley PID
Oct 2002
I need to control a steam valve 4-20mA output via a PID loop. I have a 4-20mA input from a temp transmitter.
I am using RSLogix and a 5/03 processor. Any ideas I have not used a PID loop before.
Peter
this topic has been dealt with on this forum many times before, possibly not specific to an AB plc, but I am sure that if you search this forum with the keyword PID you will find lots of threads that may answer your question
Paul
First question: How dangerous is this system you're working on? In other words, if things get out of hand, is someone likely to get hurt? Or are we just going to let off a little extra steam?
Second question: How familiar are you with the SLC-5/03 analog signals? For example: Is your input scaled from 3277 to 16384? Is the output signal scaled 6242 to 31208? If not, how are they scaled?
Third question: Is your system already far enough along so that:
1. you can monitor the input signal in your SLC? and
2. you can manually control the output by entering values into the output address?
Basically, you've got to have good inputs and outputs before you try for automatic control.
Fourth question: What is your deadline on this project? "As soon as possible" is NOT a valid answer.
Fifth question: Does your version of RSLogix500 have the Trends (graphing) feature available?
Sixth question: What is the HMI like?
A) Where are the setpoints coming from (Recipe, Operator, set-and-never changed)?
B) How much operator control will you be giving over the PID output. Auto/Man setting of CV? Auto/Man changing of Setpoints?
All of these things (can) factor into how you program the PID block. It's a bit more than just SOR PID N10:0 N10:23 N10:24 EOR.
Peter, you would do well to post the answers to the above questions, as this can generate a lot more help for you.
Fundamentally, PID loops are simply one of the many ways used to minimize the difference between a desired value (say a temperature setpoint) and the measured value (actual temperature) by manipulating an output (like % open of a valve). It was originally developed using pneumatic devices, linkages etc. but now it is primarily used as a mathematical expression inside a microprocessor (like the PLC).
The Allen Bradley SLC Reference manual actually has a fair explanation of how PID works. One of the best explanations I've seen is in the AutomationDirect.com manual for the 250 PLC. I think you can download this from their site.
I have a PIDE set up for controlling a tank level. I've run the autotune on it and it is working fairly well except for one thing. No matter...
2,289
Dear all, Please help me out in configuring the PID instruction CCW.
10,549
I am using PID first time in Allen Bradley.I have to Tune a PID on the basis of Pressure Transmitter.I have 3 pumps and pumps will run/stop...
1,670
go to work on this again this morning. I have attached the file and have a question that i can not figure out. When monitoring the temperature i...
3,537
Hi, I would like to ask about the allen bradley on how to use the pid block in the programming, the software i use is rslogix500 and model of plc...
3,884