i have a plc rack with control logix 1756-L61 (rev 12) and in the rack is the plc, controlnet card 1756-cnb/d, and the 1756-enet card.
I can go online via a rs232 cable to the plc directly.
I cannot however go online via the ethernet port of the enet card in the rack.
I am in the same ip range as i can ping and get a reply from the card but rslinx cant browse the enet card and i cant browse it in rswho.
I have my scada connected to the plc rs232 port and i would like to leave it connected and at the same time go online to the plc via the ethernet port, therefore i can see scada indication and plc bits same time.
Is there any trick to the above