UDT tags in FactoryTalk ME
xzen
Jun 2006
Oslo
97
I'm writing an application in ControlLogix 5000. The controller will have a FactoryTalk View Machine Edition HMI and communication by RSLinx. The HMI hardware and software will be acquired later in the project, so I have currently no possibility to test the controller together with the HMI.
In my RSLogix 5000 application I have an UDT (User Defined Type) called UDT_ValveStatus with the members: Open (BOOL), Closed (BOOL) and Position (DINT).
Then there are several tags of type UDT_ValveStatus: Valve1, Valve2 etc.
My question is: Can I access UDT members the same way as in the RSLogix 5000 editor? Like this: Valve1.Position, Valve1.Open, Valve2.Position etc.
Or do I have to make individual tags for each instance of Open, Closed and Position?
The Help files for RSLinx and FactoryTalk View does not give any clear answer or examples as far as I can see.
Yes you can, here is a screenshot example. PreHeaterNest is an array of UDT's. The column on the right is the contents of the UDT at index 1 in the array.
Hi
Just if you are using the parameter function you any have to type in valve_1 and not valve_1.open etc
Donnchadh
Afternoon all, I'm working on setting up a large excel recipe table for porting updates through the Linx Gateway RTD/DDE function into my recipe...
110
Hello: Today I have been testing a number of OPCUA servers with Logix symbolic client functionality. I discovered that when you create a user...
20
6,738
Hello guys, I use Tia Portal V16. What is the best way to change the indexed HMI tags when I change the format of an Udt in my plc program...
1,308
Hi All! I've created some AOI and have added a local tag of my UDT. I've set external access to Read/Write in AOI's tag browser. So, I've created...
5,744
I have never used FT View but I have a customer that is referencing a bunch of my AOI instances that are on their PLC. This is causing problems...
1,799