This forum post I found seemed to reference the same issue, and if posts were still allowed on that thread, I might make an account there to post this, but here we are.
reddit.com/r/PLC/comments/dj6r0x/rslogix5000_trends_cant_open_spcified_rslinx/f42ixbr/ RSLinx driver diagnostics showed all kinds of errors "Can't set port type to 288", "can't read port type", "harmony failed", "no harmony port for this ip address", "can't open the specified RSLinx driver" and the like. (Screenshots below) The situation was thus: I went online with a PLC in Studio 5000 using an existing .ACD file, and I wanted to create a trend for troubleshooting purposes. I was able to create the trend file, add pens, etc. but when I tried to run it, an error appeared "Can't open the specified RSLinx driver." Eh? What's RSLinx have to do with a trend? Tried changing the path within the program, tried creating a new RSLinx driver and reconnecting to it there, tried opening/closing RSLinx...everything but deleting the Harmony files, which I don't have security access to delete, but anyway, on to the path which bore fruit: Under "Select Recent Communications Path" filtering via the checkbox "Show Only Paths Matching Serial Number in Project" excluded my current path out of the list. I closed the .ACD file I was using and uploaded to a new file (I had connected using an existing .ACD) and it defaulted to a completely different file name. Saving that file, opening it, and then creating the trend using THAT file worked - I am able to run my trends, now. What a relief... Figure this might help some poor soul in the future - thanks to all for your help over the years. Cheers! |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Jul 2021
Location: RI
Posts: 1
|
This man lurked for 3 years, then made his first post as a PSA when he found a poorly-documented issue and then solved it.
Legend. |
![]() |
![]() |
#3 | |
Member
![]() ![]() Join Date: Jun 2018
Location: Lost Angeles
Posts: 2
|
Quote:
Well THIS man lurked for *counts on fingers how long ago July was...* two months, then made HIS first post a PSA about a PSA!!! Mythic!!! ![]() |
|
![]() |
![]() |
#4 |
Lifetime Supporting Member
![]() ![]() Join Date: Jun 2012
Location: Australia
Posts: 3,791
|
Just dropping in to say thanks, this helped me yesterday.
To add my 2c: I had a program called, say, "Line1Processing" that I was commissioning. Each morning I would copy and paste the program file and append today's date, so that I had a series of files from the end of each day to refer back to if needed. So my file today was called Line1Processing_20220513. Tried to run a trend and got the same error, found this post, renamed the file back to Line1Processing, and trends were all good. So it may not be necessary to upload per se, just to change the file name. I'm not sure if it was the fact that I changed the file name back to the file name that had been used for the initial download/upload, or that I changed it back to match the processor name in the program. If you were to do an upload, you'd get a file that both (a) matches the processor name, and (b) is the same file name that you uploaded with, so it could be either. |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Dec 2014
Location: Dallas
Posts: 1
|
Thank you very much.
My driver was included in the filtered list but I went ahead and uploaded to a new file and that fixed it. |
![]() |
![]() |
#6 | |
Lifetime Supporting Member + Moderator
|
Quote:
You are the definition of the saying... "Man of few words" or Lurker You joined us in 2014 but made your first post in 2022.... I would say welcome to the forum but you are seasoned ![]() But welcome anyway!
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus |
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|