ab 1756-IF16 separate dc inputs

tlona

Member
Join Date
May 2007
Location
New Jersey
Posts
33
I have an existing 1756-IF16 wired as single ended with all RTNs tied together. Channels 0-3 have 2-wire loop powered devices connected with all from the same 24vdc supply. I want to connect three (3) additional devices that are currently powered by 120v sources which provide 24vdc powered 4-20ma outputs. Do these new inputs need loop isolators being that all are powered from different 24vdc sources. Thank-you
 
I have an existing 1756-IF16 wired as single ended with all RTNs tied together. Channels 0-3 have 2-wire loop powered devices connected with all from the same 24vdc supply. I want to connect three (3) additional devices that are currently powered by 120v sources which provide 24vdc powered 4-20ma outputs. Do these new inputs need loop isolators being that all are powered from different 24vdc sources. Thank-you

The short answer is 'Yes'.

The idea is to send the 3-wire or 4-wire signal (from the separately powered devices) to one side of the isolator, while the '2-wire' part of the isolator is wired to the IF-16 like any other 2-wire device.

That said, I have yet to get that working as described. I tried what I described above with 3 different brands of 4-20 mA isolators. And I failed. I ended up adding a separate IF16 wired as 8 isolated inputs. That works fine but cost me another IF16 and another slot in my rack.

Good luck and let us know if you it working
 
I have an existing 1756-IF16 wired as single ended with all RTNs tied together. Channels 0-3 have 2-wire loop powered devices connected with all from the same 24vdc supply. I want to connect three (3) additional devices that are currently powered by 120v sources which provide 24vdc powered 4-20ma outputs. Do these new inputs need loop isolators being that all are powered from different 24vdc sources. Thank-you

It depends upon the instrument. Four wire instruments with isolated outputs should co-exist peacefully with two wire instruments on the same module, and most (but not all) modern instruments do have isolated outputs.
 
Thank-you All for the response. Yes I have some that have isolated outputs but others do not.
'thingstodo' what loop isolators did you try. I typically would use the eurotherm WV408-200 ultra slim pak II. I have not used in this setting though
 

Similar Topics

Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
2
Views
27
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
Replies
1
Views
132
Hi Guys, Hoping that someone could please confirm if the 1756-IF16/B is/isn't compatible with the 1756-L1 5550 processor(13.24). I'm sure I...
Replies
2
Views
100
Hello, friends my 1756-if16 differential connection, has been used again (almost 10 years), the measurement value of each channel of the entire...
Replies
4
Views
964
As the title suggests, I'm pretty new to control logix. Well, what I am supposed to do is connect like 8-2 wire analog sensors to this card. From...
Replies
5
Views
1,632