Powerflex 753 - How do you configure a input to reset the drive from a pushbutton ?
Cydog
Feb 2018
Maryland
313
Good Afternoon ,
Powerflex 753 seems confusing just to configure a input. A coworker installed a pushbutton to use as a fault reset for a Powerflex 753 . How do you configure a input on a Powerflex 753 , especially for a fault reset .
Thanks in advance ,
Thanks , I seen that , but I guess you need to assign a input to that , correct ?
The manual does not seem straightforward on assigning inputs.
Might suggest using CCW to look at the drive parameter list, it makes it a lot easier than using the HIM to plod thru the parameters
Wire the PB between TB1 terminals (+24V) and Di 1 and then set:
P156 [DI Clear Fault] = Port 0: P220 [Digital In Sts], bit 1 = Digital In 1 (the CCW P156 Value will state: 'Port 0: Digital In Sts.Digital In 1')
Basically, the on-board processor will monitor bit 1 of P220 which monitors the voltage applied onto the Di 1 terminal of TB1; upon receiving 24VDC at the TB1 Di 1 terminal ('false-to-true transition') any present fault(s) will be Reset.
I agree that the manuals are pretty vague about assigning on-board I/O functions...Oh well...At least you're not dealing with Siemens English manuals...:D
How to remove faceplate from power flex 753 and not shutting the system down. What parameters should i change?
101
Hi all, I am having a problem with a powerflex 753 we have on site and keep getting input phase loss. The drive has been running for a long...
1,334
Hello Friends, We have a powerflex that stopped working sometime last week. It doesn't communicate over the network, or use CCW directly from my...
437
Hello all! I am fairly new to the world of PLC's and this forum, so I apologize for my lack of knowledge. I have a Powerflex 753 that keeps...
543
I am bench testing a PF753 (20f11nd096aa0nnnnn). I replaced the IGBT's and IC's in the firing circuit. Upon power up, I get the STS light...
711