OT: Keeping water out of impulse line

TheWaterboy

Lifetime Supporting Member + Moderator
Join Date
May 2006
Location
-27.9679796,153.419016
Posts
1,924
I have an issue where I have a DP transmitter on a horz tank reading liquid level.
Due to odd and unforeseen circumstances the tank filled to the top above where the transmitter is connected and so it allowed water into the low side impulse line to the Transmitter which threw everything off of course.

Is there a readily available solution to this? I came up with the idea of using a hydrophobic filter, a membrane style gauge isolator, a water trap like those on compressed air lines, and simply taking the impulse line above the top of the tank to prevent the siphon from ever occurring, like an inverted P-Trap.

I can’t change the pressure tap location so I have to deal with what I have.

But before I fall back on my training from the Rube Goldberg School of Engineering, I wonder if there is already a bolt in solution available for such conditions?
 
Yield to the force: fill the upper tap with water and leave it that way. You will have to recalibrate of course.

(edit: tap not trap, and added the need to recal )
 
Last edited:
Don't think I want to trap water up there, just need it to not be able to go into the low side. So an upward loop would work, and is the only viable option I can think of.
 
Don't think I want to trap water up there, just need it to not be able to go into the low side. So an upward loop would work, and is the only viable option I can think of.

Not sure what you mean by low side. Can you make a sketch?

Even if you do everything you can to prevent liquid water out, depending on the conditions, water vapor may condense and you could get water in there and not know it, which will throw off the calibration. This is a more common problem in plants with steam, but it could anywhere. Ensuring the upper tap is full of water to a known elevation is the solution: it is better to know the densities and heights of the fluids on the traps, water or air, than to not be sure

My dad ran large stream turbine thermodynamic heat rate acceptance tests to an accuracy of a quarter of a percent, and pressure measurements were a critical part of that, and this was the solution.
 
You already got it, an upward loop would work.


That along with a drop leg below the low side port elevation with a drain valve.
 
What is the pressure in the vessel space above the water?

Is it a vacuum, a positive pressure, or open to the atmosphere?
 
If you go with the condensate leg below the DP unit to keep condensate from affecting the measurement, then that will require a regular maintenance task to open the valve daily or weekly or monthly or after an event.

Or we could steal @Tom Jenkins' idea and put the float valve after the condensate leg to drain it.

Or put another DP sensor on the impulse tube to generate an alarm when it gets water in it.

To be fair, you mentioned Rube Goldberg first ;)
 
It's in a pressurized tank (130-ish psi) so internal maintenance of a float would be a problem, plus vapor condensation would still be a potential issue.

Emerson sent me a flyer for a set of transmitters that are DP but connected by wire so no tubing at all. Interesting option.

I went with the high loop and condensate drain, It will be tested today. :oops:
 
You could also of course result to 2 gauge transmitters and a bit-o-math.

That is what the emerson device would do for you.

The issue with 2 transmitters vs 1 is that 2 will possibly less accurate than one due to summation of errors. It really depends on how accurate you need and if you can easily get there with 2.
 

Similar Topics

Need to add new tags to some recipe inside a Wincc Tia Hmi . Do we have an option to download the recipe , with the newly added elements ...
Replies
0
Views
244
Hi, We have a machine that's fairly new on site, but has been designed fairly badly from a controls perspective. One of my concerns is that the...
Replies
14
Views
3,218
Hi, We have an application with a very peculiar problem with a multi-state button. In the button both the value and indicator are set to the...
Replies
2
Views
1,679
Hello guys and gals, I have been researching the last couple of days for a formula for hiring and keeping employees long term. There are plenty...
Replies
33
Views
14,502
We have a CPU S5 115 with an OP 25 . Can we replace the OP25 by a new hmi touch panel? which type? Communication is done using V24/TTY-interface...
Replies
12
Views
2,453
Back
Top Bottom