Hello guys, I have a big problem with communicating with my drives.
I cannot send a Control word and Main Reference Value to my drive.
I'm able to monitor the inputs/outputs and the strange thing is that I can see my Status word and Main Actual Value (0607 = drive in stopped). If I operate the drive manually, I can see the STW and MAV changing... When I monitor the input/output modules in the drive, I can change the CTW (047F = to start drive) but nothing happens!
Setup:
S7400 CPU (6ES7416-3XR05)
IM467 (6ES7467-5GJ00)
Danfoss VLT500 drives
PCS7 7.1 control system
I have connected my drives to the IM467 module.
The IM467 module is operative without errors, the same goes for the drives. The CPU gives a message:
"more than one write data record (0 data records) has accumulated on the DP master. i.e. the DP master is temporarily working more slowly on the P bus than the CPU."
It has to do with the IM467 module.
The steps I have taken are as follows:
1. Installed GSD file from danfoss (DP0) (da030402.gsd)
2. Added drives to the hardware configuration and added PPO Type 5 Module consistent (also tried Type 5 Word consistent and Type 3 Module consistent)
3. Assigned the inputs to process image PIP1 and outputs to PIP2.
4. PIP are assigned to OB35/34 and called in CFC editor (PCS7 7.1 environment)
5. Bus address is configured
6. I set the following parameters:
Protocol = DP
Baud rate = 1.5 = same as master
Bus address = same as configured in hardware configuration
PPO Type 5 is selected
Function of control word bit 10 = Bit 10 = 1-> CTW active
Drivemode = Remote
Can anybody assist me on this? I've been busy with it for over a week now still no improvements...
Thank you,
Best regards,
I cannot send a Control word and Main Reference Value to my drive.
I'm able to monitor the inputs/outputs and the strange thing is that I can see my Status word and Main Actual Value (0607 = drive in stopped). If I operate the drive manually, I can see the STW and MAV changing... When I monitor the input/output modules in the drive, I can change the CTW (047F = to start drive) but nothing happens!
Setup:
S7400 CPU (6ES7416-3XR05)
IM467 (6ES7467-5GJ00)
Danfoss VLT500 drives
PCS7 7.1 control system
I have connected my drives to the IM467 module.
The IM467 module is operative without errors, the same goes for the drives. The CPU gives a message:
"more than one write data record (0 data records) has accumulated on the DP master. i.e. the DP master is temporarily working more slowly on the P bus than the CPU."
It has to do with the IM467 module.
The steps I have taken are as follows:
1. Installed GSD file from danfoss (DP0) (da030402.gsd)
2. Added drives to the hardware configuration and added PPO Type 5 Module consistent (also tried Type 5 Word consistent and Type 3 Module consistent)
3. Assigned the inputs to process image PIP1 and outputs to PIP2.
4. PIP are assigned to OB35/34 and called in CFC editor (PCS7 7.1 environment)
5. Bus address is configured
6. I set the following parameters:
Protocol = DP
Baud rate = 1.5 = same as master
Bus address = same as configured in hardware configuration
PPO Type 5 is selected
Function of control word bit 10 = Bit 10 = 1-> CTW active
Drivemode = Remote
Can anybody assist me on this? I've been busy with it for over a week now still no improvements...
Thank you,
Best regards,