Hi all
I have a project to convert a Micrologix1500 with onboard IO and IO extension modules to a Compactlogix 5069_l306ER with 2 local 16point IO modules to replace the Onboard IO and the original IO extensions hanging on an AENTR.
I have run the SLC program through the Conversion Tool and created a CLX program (FW v31) and added the new IO.
The Local IO data structure is new to me so I have a question regarding addressing the .Data (Bool) part of the IO information so that I can Buffer the IO data using CPS instructions.

My first stab at setting up the CPS Instructions is
for the IPs
Source: Local:1:I.Pt00.Data[0] (Channel 0 Bool)
Dest: IP_Buffer_Loc_1.0 (bit 0 of a Dint)
Length 16

And for the OPs
Source: OP_Buffer_Loc_2.0 (bit 0 of a Dint)
Dest: Local:2:O.Pt00.Data[0]
Length: 16 (only copies bits 0 to 15 of the Dint)

or is there a better way to buffer the IO

Thanks
Ian
 
On the older CPLX systems, the I/O data was individual bit of a word or Dword.
Now on newer controllers they are stand alone bools.
So I don't think you can move them all at once anymore. You have to do each one individually. I use Structured text for the mapping. I have seen others do it with one rung of ladder per IO point. ST is faster.
 
Hi Ken
thanks for your reply.
Oh well back to the drawing board. at least I only have a few 16 bit IO cards to deal with
Cheers
Ian
 
You could create an aoi to do the moving of values into your dint bits. This way you only have to do the work once.
 

Similar Topics

I am very new to Modbus and the industry, so forgive me if I am missing something obvious. I have known Modbus register addresses coming from a...
Replies
7
Views
227
I have a system using Rx3I CRU320 redundant CPU with Proficy Machine Edition Software. In the hardware configuration of each CPU module, under...
Replies
14
Views
388
See the screenshot of EIP tag list. We are trying to read in a digital input that is hard-wired. It is shown here as I31.1. I believe we cannot...
Replies
7
Views
282
Hello all. I have a Simatic SM374 (374-sxh01-0aa0) sim module. I am using TIA portal v.18. I can't find this module in my list of hardware devices...
Replies
12
Views
754
Hello, I have a device with 68 words input. But one block on the Devicenet Scanner is only 61 words. I am trying to map this device to 2...
Replies
3
Views
531
Back
Top Bottom