timer TOF (plc siemens S7 200) (...214)

paris

Member
Join Date
Oct 2006
Location
PARIS
Posts
55
how to make a timer TOF with S7 200 CPU 214 this S7 200 does not have a timer TOF,
it y' has only TON and TONR
thank you
 
Paris,

I remebered this issue has been dealt with in the tips and tricks for the S7-200. I knew I had them lying around somewhere, but in the end had to google the net for it, because I couldn't find them back. It's tip 31, which can be found here. This tip deals with off-delay timers, pulse timers and extended pulse timers, all of which are not present in the older S7-21X PLCs.

Kind regards,
 
Paris,

the input for the timer should be 'NOT M1.0' in stead of 'M2.0'. Then it will work.

Kind regards,
 