bill2bhappy
Member
I have a head scratcher I have a PID in auto that is getting the external SP. The internal SP is zero I have looked for something writing to the internal SP and there are no other references in the software. This is in PME 8.6 with the SIM 16 installed online with a CPE-310. The PID is enabled, in auto, not in override, the high clamp is 32000 counts the low clamp is 0 counts, SP range is 0-1400 (SCFM) for a flow controller and the external SP into the PID is 80 (SCFM) does anyone have any other ideas of what to try? I have a case in with GE but been waiting to hear back with a high priority for a while thought someone else might have some ideas.