WAGO 750-881 and Biejer X2 Modbus / tags question

Join Date
Aug 2019
Location
Queensland
Posts
3
Hey Guys,

Im trying to work out the Modbus memory map and the tags on the Beijer x2 HMI and 750-881 WAGO PLC. Have looked up the forum and found some great info but I'm just a little confused and also new to it. The 750-881 modbus register mapping conflicts with what i appear to be finding.

%IX0.0 -> Modbus Input address of 10000 (0x1000) which works but the documentation says it a configuration register?.

%QX0.0 ->Modbus Coil address of 00001 (0x0001) which i cannot get the HMI to read at all.

%MW0 ->Modbus holding address of 30000. (0x3000) which i actually found my AI data. Which displays on the HMI fine.

Think I've managed to confuse myself over this last week, so hopefully I've just overseen something simple. Im also trying to change some bits in a word at 1400 (0x300) but the HMI will not except that register location at all?.

Any suggestions would be great, thanks heaps in advance! :)

750-881 modbus.png
 
Hey Garry,

Thanks for your help, much appreciated, I worked out and can read Input, coils and input registers now. I got a feeling my Bieger x2 panel is not working correctly as Im having trouble trying to write/change bit to memory %MX or unused %QX coil registers. Tried for the life of me to export my tags on codesys 2.3 which would make life so much easier but the tag input on iX won't read the .exp file correct. Just got to get this writing thing sorted and ill be happy, good challenge.
 
Hello, Could you help me in connecting my Wago 750-881 with a Beier X2? There is communication because I have no fault on the Beijer, If I search inside the Codesys 2.3 I can See the IP of the HMI, but it gives an error. Tried in the IX Developer the Wago setting and a lot of other, like the Codesys, just cannot get them to
work together. Could you help?
 

Similar Topics

Hi, I have never used modbus communication in Codesys 2.3, any tips and tricks are much appreciated. The system is a Wago 750-881 that controls...
Replies
3
Views
1,836
Hello, Maybe it is just a simple problem, but I cannot solve it. I have a Wago 750-881 connected to a Beier HMI through IP TCP, the connection is...
Replies
0
Views
891
Hello, I am new to WAGO PLCs and e!****pit. I am struggling to program a 750-881 PLC since I am unable to see/add an application under the...
Replies
2
Views
2,340
I'm facing a problem with the 750-881 Controller of Wago. I created a visualisation ( page named plc_visu ) en it'shows up in the webbrowser. It...
Replies
1
Views
1,711
Doing a project that will have Wonderware for our HMI. Is it possible to use Wonderware's OPC to communicate with WAGO 750-881 plc? I would think...
Replies
5
Views
1,922
Back
Top Bottom