Old August 11th, 2017, 01:48 PM   #1
RogerBrunner
Member
United States

RogerBrunner is offline
 
Join Date: Feb 2017
Location: Florida
Posts: 38
Emergency device

I think it is against NEC/NFPA code to wire a emergency device thru a software relay (PLC), although I unable to locate the code. If the software fails the emergency device will not work. Any suggestions or ideas on this? I seem to recall some sort of code when i was installing fire alarms.
  Reply With Quote
Old August 11th, 2017, 02:15 PM   #2
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 356
http://www.plctalk.net/qanda/showthread.php?t=35637

This thread may give you what you need!
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old August 11th, 2017, 07:01 PM   #3
Timbert
Member
United States

Timbert is offline
 
Timbert's Avatar
 
Join Date: May 2011
Location: The middle of the Pacific Ocean
Posts: 346
Short answer is yes PLC devices can be used in emergency stop circuits.

Slightly longer answer is that all devices involved in emergency stop and other functional safety circuits must be rated for such use and installed properly.
__________________
An expert is a man who has made all the mistakes which can be made in a very narrow field. --Niels Bohr as quoted by Edward Teller
  Reply With Quote
Old August 12th, 2017, 04:00 AM   #4
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,539
Quote:
Originally Posted by Timbert View Post
Short answer is yes PLC devices can be used in emergency stop circuits.

Slightly longer answer is that all devices involved in emergency stop and other functional safety circuits must be rated for such use and installed properly.
To expand on Timbert's comment:

If you run your Estop through just any old cheap PLC, you're in for trouble. If you use a Safety PLC, and use it as indicated by the manufacturer, then it is probably OK. Siemens has the F (failsafe) PLCs, AB has Guardlogix, I'm sure other brands have them as well, in addition to smaller standalone safety controllers.

To OP: Sorry, I don't have references to specific codes.
  Reply With Quote
Old August 12th, 2017, 11:10 AM   #5
QvixoteRoux
Member
Mexico

QvixoteRoux is offline
 
Join Date: Jun 2014
Location: Reynosa
Posts: 70
Its complete against current NEC/NFPA regulations

all safety input devices (e-stop, interlock, light curtains, two hands, other) must be wired to a certified safety control, they cant be neither used directly to control lets say a motor, directly wiring the motor supply into the e-stop

Rokwell has a nice safety handbook hat you can get for free (even phisical book) from their website
__________________
Mexican, need to practice engrish, please cooperate

Industrial Engineer working as PLC programmer.
---
"Everybody believes what is easier for them to believe"
  Reply With Quote
Old August 15th, 2017, 09:20 AM   #6
RogerBrunner
Member
United States

RogerBrunner is offline
 
Join Date: Feb 2017
Location: Florida
Posts: 38
Thanks for all your input. I'm not controlling machines. We are controlling access into communities, the 1st responders have a "key" that will open the barrier gates, that key is the emergency device that i believe should be hardwired into the gate controller and not run thru the PLC. I just can't locate a code in NEC/NFPA.
  Reply With Quote
Old August 15th, 2017, 11:56 AM   #7
Steve Etter
Lifetime Supporting Member + Moderator
United States

Steve Etter is offline
 
Steve Etter's Avatar
 
Join Date: Apr 2002
Location: Morristown, TN
Posts: 897
Take a look at Fortress. They have keyed systems that can include safety-rated switches. They should be able to supply keys and locks to accomplish this.
  Reply With Quote
Old August 15th, 2017, 12:11 PM   #8
George Graziano
Lifetime Supporting Member
United States

George Graziano is offline
 
Join Date: Jul 2004
Location: NY
Posts: 410
My last job had 2 gates. They both had installed on them a sensor so that a Siren triggered them open. One of the Electricians was a Volunteer Fireman (Chief)so he had a siren on his truck and would test it at intervals. There was also a lockbox used by Emergency Personnel that had a passkey in it.
George
  Reply With Quote
Old August 15th, 2017, 02:06 PM   #9
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,311
There is nothing in the NEC (NFPA 70) about that. There might be some other NFPA document on LV emergency / alarm systems, such as NFPA 72. But enforcement of things other than the NEC is generally hit and miss in many places. The first place I would check though would be the local Fire Marshall, since they are generally the First Responders. NFPA 72 article 17.3.2 says that the functionality of any "initiating" system must be acceptable to the AJH (Authority Having jurisdiction). That's for fire / safety alarm systems, but it likely applies to this too, if anything does.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
VEGAFLEX 61 Level Transmitter alexFSC LIVE PLC Questions And Answers 3 December 18th, 2014 04:18 AM
PROFIBUS device configuration using a PLC arbj LIVE PLC Questions And Answers 4 March 1st, 2014 11:53 AM
PLC dummy needs help picking a device thaukom LIVE PLC Questions And Answers 4 December 11th, 2013 10:50 PM
Does any relation between Sinking/Sourcing PLC inputs and NPN/PNP sensors? Tofo LIVE PLC Questions And Answers 27 December 11th, 2013 02:26 PM
Help Need !!! think & Do , ABB Robot , Device Net , Flex I/O jim-garcia LIVE PLC Questions And Answers 2 August 6th, 2010 07:19 PM


All times are GMT -5. The time now is 03:16 AM.


.