DH + Question

kbradray

Member
Join Date
Jan 2006
Location
Columbia
Posts
175
I have a SLC 5/04 and I want to put it on a DH+ network. I am using a controllogix bridge to get from my business network IP subnet to my plant floor IP subnet and a DHRIO card. The DHRIO card is set up on Channel A communicating with a PLC 5. I want to use Channel B to start a new DH+ network.

Question 1. The node address for the SLC 5/04 is 1… What is the node address of Channel B? Will there be any conflicts?

Question 2. What is the default node address of SLC processors and older PLC 5 processors.
Question 3. Can a node address of a PLC on a DH+ network be changed by navigating to the processor via the network, or does one have to plug directly into the processor (in my case) via DH 485


At this time I would like to leave the node address of the SLC because it is in full production and I don’t want to take it in to program mode (down) to make changes at this time. I was hoping to put it on the network with out any downtime.



Thanks in advance for assistance.
 
kbradray said:
I have a SLC 5/04 and I want to put it on a DH+ network. I am using a controllogix bridge to get from my business network IP subnet to my plant floor IP subnet and a DHRIO card. The DHRIO card is set up on Channel A communicating with a PLC 5. I want to use Channel B to start a new DH+ network.

Question 1. The node address for the SLC 5/04 is 1… What is the node address of Channel B? Will there be any conflicts?
You may have different processors with identical node addresses as long as they are on separate channels.

Question 2. What is the default node address of SLC processors and older PLC 5 processors. Default is always node 1

Question 3. Can a node address of a PLC on a DH+ network be changed by navigating to the processor via the network, or does one have to plug directly into the processor (in my case) via DH 485
You may change it via the network.


At this time I would like to leave the node address of the SLC because it is in full production and I don’t want to take it in to program mode (down) to make changes at this time. I was hoping to put it on the network with out any downtime.



Thanks in advance for assistance.

BAKLAVA!
 
But, really, there's no reason that the SLC cannot live on the same network as the PLC5. You just need to make sure that everything is wired properly and that all addresses are unique on the network.
 
Thanks

Thanks all

I did just put it on channel a along with the PLC 5. Everything is happy and on line. I will change the node address whenever the machine is down and I will not bother production.

Thanks again.
 

Similar Topics

HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
45
I'm working with a project that contains some routines in ST but mostly in ladder. Am I correct in assuming this 'rung': DB1001DO._01AV55_OPEN :=...
Replies
4
Views
84
Is there a way to reset the count on the RS Logix BackUp?? XXXXX PROGRAM IN PROGRESS_BAK445.RSS XXXXX PROGRAM IN PROGRESS_BAK446.RSS XXXXX...
Replies
8
Views
245
I have a few questions about Studio5000. 1. Why is my RA folder so big? its well over 100 GB. 2. How do you delete versions or extra files...
Replies
3
Views
269
Currently we have a fat( I think that is what it is called) Intouch application. An application resolution of 3840x1080, and inside that 2x...
Replies
0
Views
84
Back
Top Bottom