Error message $006 Transfer Fail OP15

VDBSYS

Member
Join Date
Sep 2003
Posts
4
Dear readers,

I'm having troubles with my OP15.
To put the panel in transfer mode, you press the esc-key, the arrow right and the arrow down-key at the same time, and then you apply the power.
Normally the panel displays "Ready for transfer".

But today, it said "$006 Transfer Fail-No : 0 Sts: 8"
I tried the same routine a few times, but with no result.

Has anyone seen this message before ? And what is the solution to
get it in transfer mode ?

Kind regards,

VDBSYS
 
Hi,

the manual say's:

$ 006 Error during data transfer in Download
mode

(message with two variables)
Var. 1 Status display
Var. 2
1 Internal error
3 Timeout error
5 Parity error
6 Framing error
7 Overrun error
8 Line interruption
9 Receive buffer overflow
10 Wrong control character
11 Internal error
Check connection, repeat download

HTH

regards

Rolf
 
I know ... but why ?

When I apply tension to the OP, (no cables connected),
he starts up, and then giving me the message.

So I don't understand why they give the term 'Line interruption'.

Thanks anyway.
 
ERRO $006 on OP15

Hello VDBSYS,

I just read the question you have post 2 years ago.

'OP15 was giving the $006 transfer error'.

Did you ever solve this problem ?
I am actually facing the same issue and I could use your knowledge.

Thank you in advance


Marc

[email protected]
 
Dear Marc,

Indeed, I solved this problem ... I contacted Siemens about this matter and theu told me to connect the cable between your OP and Pc and then apply power to the OP. When the OP comes in transfer-mode, he will search a communication partner ... if he doensn't see anyone at the end of the line, the OP will give this error ...

So try this and if you need more help ... [email protected]

Good Luck,

Bert
 
Dear readers,
Using ComText:
I'm having troubles with my OP15.
To put the panel in transfer mode, you press the esc-key, the arrow right and the arrow down-key at the same time, and then you apply the power.
after testing RAM,Flash ---> Test OK (the error meassage is appears)

"$006 Transfer Fail-No : 0 Sts: 8"
i don't know if the cable is ok or not ?
if you have the ComText Manual and Drwing Cable please send me :
[email protected]
 
I am getting this error as well. I can download to the OP15, Comtext reads "Transfer Complete". But after I unplug the comm cable the same error message pops up ($006 Transfer Fail-No : 0 Sts: 8) on the OP.

This is a new OP15, and the message was not on the display prior to my first attempt to download to the OP.

I am using the PC/RS232 to AG/TYY adapter and the program appears to be transferring on both the PC/PG and the OP.

Any ideas?
 
Last edited:

Similar Topics

Hi guys, I have the same program in my CPU and in my SD card but when I boot from the SD card I get error message 2400 which relates to some...
Replies
4
Views
596
Good day I would be so glad if anyone can assist me. I have a message instruction and i am sending data between 2 PLC's. The Message...
Replies
5
Views
2,852
I have uploaded a file from a panelview and i get a message when trying to restore it: "This runtime application file was saved in a protected...
Replies
4
Views
1,323
I have been working on creating a subroutine for my company to send an email from my controller to our email server and had been successful in...
Replies
12
Views
2,372
I have a 1756-L62 that is sending a message to give a 1769-L24ER a permissive bit to run. This system has been working fine for about 2 years...
Replies
4
Views
3,419
Back
Top Bottom