I'm thinking of trying to communicate information (counters, data integers/v memory) from a directlogic PLC to an allen bradley slc504. my question is would ethernet be the best way and any tips on if it's even compatible to do.
 
The SLC 5/04 CPU family does not support Ethernet communications; only the latest, SLC 5/05 series, allows it.
Since the AutomationDirect PLCs provide only Ethernet and Serial communications options I guess you will probably have to run Modbus RTU on a RS-232/422 network; for the SLC 5/04 end you will need a communications module such as the ProSoft MVI46-MCM (http://www.prosoft-technology.com/content/view/full/135)
On the DL side, if wanting to establish a peer-to-peer connection you might need a supplementary communications module; otherwise, most of the DirectLogic CPUs on-board communications ports could communicate as a slave Modbus RTU node.
 

Similar Topics

Node 1 and 2 can share alarms to the other 10 or so view nodes. It has been working fine for months after an upgrade to Windows 7 and InTouch 11...
Replies
2
Views
3,402
Hi everyone, I am working on a project that needs to expose the SV (Set Value) of a temperature controller to a SCADA system. SCADA <-...
Replies
4
Views
134
Hi, We don't do many Rockwell projects but recently did onw with a Control Logix and Panelview. What files do customers expect when you send...
Replies
4
Views
214
Hi, I recently acquired a micro830 48qwb, and it has relay outputs bult in. For outputs 0-6, they all use 24vdc. To save on space and terminal...
Replies
1
Views
1,479
Hi, I'm challenging myself to install a PLC for the first time. I went for a Micro830 48QWB, since it has 48 I/O and free software (CCW). From my...
Replies
3
Views
1,941
Back
Top Bottom