Cradlepoint and Ethernet Tunnel
Killer K
Aug 2017
Southbury
Just wondering if anyone ever had this setup. I have 3 micrologix 1400 communicating via cradlepoint modems. They in turn each is hooked to a Ethernet tunnel. I am able to hook up to any tunnel and I am able to go on line with any PLC. Can make changes if need too. Right now MSG works from 1 PLC to the main PLC. But not the other. Even thought I have communications to the PLC does that mean the MSG, if setup correctly, will work?
Welcome to the PLCTalk forum community !
This is not necessarily an easy answer, so let's fill out the details. I think you're describing a "main PLC" and two remote stations, and an engineering computer located at the main station.
Station A: MicroLogix 1400
Station A: Engineering Computer
Station B: MicroLogix 1400
Station C: MicroLogix 1400
The "Ethernet Tunnels" are probably virtual private networks between any two of the Stations.
Can you provide examples of the network addresses in these cases ?
You may need to enable network bridging between the different VPN adapters that are running the "tunnels" between the Cradlepoint devices.
Thanks Ken.
No computers involved. The Main PLC Micro 1400, located at office, is connected to Ethernet tunnel (trusted) and the (untrusted) is connected to the modem. Modem gives access to the other 2 Remote PLC Micro 1400, out in field, same setup. The main is just getting levels from both and then outputting signal to chart recorders in main control room. Nice easy setup. Like I said one was already working and still does. I just duplicated the remote panel working to the other remote panel.
addresses use PLC 192.168.7.110, 1192.168.7.120, 192.168.7.130
connected (trusted) 192.168.7.112, 1192.168.7.122, 192.168.7.132
Modems Main 192.168.0.10, the other 2, obtain address
Thanks Ken.
Can you ping between the 2 processors you are trying to message between?
That will answer if it's a network connectivity issue or an issue with the messaging setup/programming in the controllers. I would try that first if possible.
Hey all,
Thanks for any help given. Just an update. I was able to ping all three PLC's. Allen Bradley sent me a Tech note: 751108 to resolve this issue for RSLogix 500. Was able to get messages working. Thanks again
Now i try to open a different project and get unsupported processor go to a higher version.
Never ending
Hi all, I have a client that has a water tank with a loop powered level sensor; the 4-20mA loop goes through a telephone line, half a mile away...
26
6,976
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
80
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
257
Hi all, My ethernet port on my laptop recently broke and I was hoping to just use a usb-c dongle in the mean time to go live on my PLC until I...
453
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
16
499