SLC 5/03 Fault 252h
Spencer.hall
Jun 2019
Florida
New user here with an 252h fault code. I've tried clearing the fault but it's persistent. Trying to check what should be causing this and how to resolve it.
Welcome to the PLCTalk forum community !
On SLC-500 controllers, the first two bytes are a Slot number that's causing the fault, so the problem is in Slot 02 (the CPU is Slot 0).
Chapter 16 of the SLC-500 Instruction Set Reference Manual (1747-RM001) shows that Error code 0x**52 indicates that a module that is in the user program is not being detected by the CPU.
A good way to troubleshoot it is to go into the S:11 and S:12 Status bits and disable the Slot. If the fault is then clearable, then it's the module hardware. If the fault moves to another slot number, then it might be the backplane.
Hello all! I have some machines that run an SLC 5/03 and occasionally a fault is generated. Recent Example: A power supply wasn't screwed in...
419
hello at work we have a machine controlled with an SLC 500 fixed, model 1747-l30c at fault, i plan to migrate to a micrologix controller. I'm...
3,009
Has anyone ever seen this fault or have any insight as to what it was. I found this on an SLC 505 after we had the main breaker off working in...
1,411
Hello everyone, I got called down to a plant to service a powdered metal press. It has an SLC 500 5/02 CPU that was faulted for the code 0002h...
1,792
Hello! We have a drum rotation machine controlled by a AB SLC 500. The drum rotation inputs comes from a encoder into a 1746-HSCE. We are using 2...
1,134