plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old June 24th, 2019, 09:14 PM   #1
kalabdel
Canada
kalabdel is offline
Troubleshooting single phase motor intermittent tripping breaker
Good day everyone,
Single phase motor,3/4 Hp, capacitor start, dual voltage wired for 115VAC with Allen Bradley reversing contactors and 10 amp circuit breaker. It runs a machine via V-belt and very simple mechanics.
It intermittently(could be weeks) trips the breaker and after resetting the breaker everything works fine for days and often weeks.
I have two such cases on two different sites and one customer provided specific information regarding their motor (the machine is two months old/new) that it tripped after having moved for a 7-8 seconds. Not on start-up. And I can eliminated the possibility of mechanical cause.
I've had similar problems over the years and always were resolved after a few trips by replacing the motors but would love a more knowledgeable approach to troubleshooting.
  • What tests can I perform on the motor?
  • If the centrifugal switch does not open after the motor reaches the required speed what happens, how is the motor, capacitor, winding etc. affected?
  • I removed the capacitor cover and the capacitor looked quite good but there was a very thin layer of red dust sort of like rust that was inside the cover and also on the part of the motor that was covered by the capacitor cover. Could this have come from inside the motor though the 1/2" hole the capacitor wire go through? If yes what would it be?
Old June 24th, 2019, 09:30 PM   #2
duckman
United States
duckman is offline
If the centrifugal switch doesn't throw out, the start winding stays in the circuit so both run and start are pulling current, so that is a very likely cause of the over current.
You should hear the switch click back in place when the motor slows and when after getting up to speed.
Old June 24th, 2019, 09:41 PM   #3
kalabdel
Canada
kalabdel is offline
Thaks ducman. How long would you say it would run without the switch opening before tripping the breaker? I think the motor draws 8 Amps and the breaker is 10 Amps.
Old June 24th, 2019, 09:45 PM   #4
Cow
United States
Cow is offline
Your breaker is undersized. Who determined it needed a 10 amp?
Down here in the states, the NEC considers that a 13.8 amp motor at 115 volts.
We'd probably try it on a 20 amp breaker first, with the option to take it up to a 35 amp breaker if necessary due to starting issues. The NEC would even allows us to go even higher if it still had trouble starting.
Old June 24th, 2019, 09:48 PM   #5
kalabdel
Canada
kalabdel is offline
The manufacturer of the equipment. It's was bought and installed as is about two months ago. I will contact them in the morning and ask that question.
Old June 24th, 2019, 11:01 PM   #6
kalabdel
Canada
kalabdel is offline
Sorry, my mistake. the motor is 1/2 Hp.
Old June 25th, 2019, 02:38 AM   #7
BryanG
United Kingdom
BryanG is offline
Unless you get some data you are just guessing. Connect a logger to the system that will store current and preferably voltage against time, sampling maybe every second. You can buy off the shelf units, or you can make your own with a spare PLC. Better still if you could trigger the logging as the motor starts, then you could grab the data with a higher frequency and not run out of storage.
__________________
Knowledge is power, share the knowledge.
Old June 25th, 2019, 06:16 AM   #8
EICS
Australia
EICS is offline
EICS's Avatar
not sure about North American electrics but in Australia the standard curve Breaker is a C Curve for general Applications, for Motor starting a D Curve Breaker is recommended as it has a longer time delay curve for motor starting applications.
the Breaker is designed to protect the Cable so it should be sized for this NOT the Motor, the motor is protected by a Thermal (or Electronic) Overload.
check if its a Motor Starting Breaker as if its a general purpose that could be you intermittant tripping issue.
Old June 25th, 2019, 08:00 PM   #9
kalabdel
Canada
kalabdel is offline
Quote:
Thanks Bryan it sounds like a good project. I've been thinking of something of that sort and prefer your latter suggestion with PLC just need to make it as compact as possible and versatile to reuse with similar issues.
Old June 25th, 2019, 08:08 PM   #10
kalabdel
Canada
kalabdel is offline
Quote:
Thanks EICS. I posted a link to the datasheet in my first post and it is general purpose for sure.
From the datasheet;
"The CLB-Series is a compact, single pole, push-to-reset family of thermal circuit breakers designed to protect
equipment. Utilizing simple, precision design with few moving parts, these breakers offer cost effective,
extremely reliable circuit protection with high resistance against shock and vibration."
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Single phase motors kalabdel LIVE PLC Questions And Answers 11 April 30th, 2019 07:40 PM
Mechanical/Material Handling and ISA 88 rlmunoz LIVE PLC Questions And Answers 7 October 11th, 2018 08:45 AM
Motor for single phase drive basharath LIVE PLC Questions And Answers 3 August 7th, 2014 02:54 PM
Automation or not ? Pierre LIVE PLC Questions And Answers 23 May 26th, 2004 06:06 AM
Soft starter vs Single phase motor Pierre LIVE PLC Questions And Answers 13 January 25th, 2003 10:05 PM