Beckhoff CX8090 ERR LED and X101-102 ports not working

karakaya_o

Member
Join Date
Jun 2019
Location
Turkey
Posts
1
Hello there,

I have a problem with the cx8090. When I insert the plug to wall, the err led lights up steadily and does not go out. I copy to sd card new update. I dont know the IP adress of the device. I could not access the device with IP. I want to give a new IP address. But X101 and X102 ports lights are never blinking. X001 is blinking green and yellow. I don't understand the source of the problem. Thanks for help.
 
Port X001: ethernet -> mainly for programming and ADS-communication

Port X101 en X102: ethercat; IO-communication

the manual

https://download.beckhoff.com/download/document/ipc/embedded-pc/embedded-pc-cx/cx8090_hwen.pdf

page 59:

green on: (ethernet) link present
yellow blinking: activity.

--> the cpu is communicating with 'somebody'

Standard configuration is DHCP.

But is the cpu 'new' of is it an excistion configuration.

ERR-led: error or boot-diagnosis led > RED?
Is the error-led RED and steady on?
 
Last edited:
If that manual is correct,
There is a set of D.I.P. switches on the front of the PLC. Chapter 6,
Parameterizing and commissioning, starts out with how to set the
switches for DHCP and an IP address - which can be changed programmatically.

There is also Error handling and diagnosis in Chapter 9.

Good Luck.
Poet.
 

Similar Topics

Hi to everybody. I'm beginner on Beckhoff so I'm having issues with connecting Beckhoff CX8090 and Weintek EMT3070a. I'm trying to use Beckhoff...
Replies
2
Views
1,724
Good afternoon! I have problem with connection 3d-party device to beckhoff CX8090. The device is Festo CTEU-EC module(EtherCat). After auto scan...
Replies
6
Views
3,882
Hello folks! Long time lurker here, my first post so be gentle.. We recently replaced a beckhoff cx8090 controller.. and i was asked if i could...
Replies
8
Views
2,938
I am going to attempt to use a EL5151 and EL5101 to read a torque flange (freq output) and encoder. I need to be able to do calculations that...
Replies
4
Views
1,616
So, I got this Beckhoff embedded PC for some testing purposes of various K-bus terminals. Before I worked with CX1010 and had no such problems...
Replies
9
Views
11,922
Back
Top Bottom