Online Editing with RSLogix500 disappeared

plcman777

Member
Join Date
Oct 2004
Location
Wa.
Posts
25
I lost my ability to do online edits to my SLC5/04.

I did online edits for three days in a row, then on the fourth I was no longer able to do online edits.

I checked all the places I could find in the help files to enable online edits and they are enabled.

Any ideas why suddenly I no longer have the option to online edit?

Thanks
 
I think you may have leftover edits from previous online sessions. Make sure to assemble or cancel past edits before editing again.
 
there is a BIT in the S2 file somewhere that needs to either be set or reset to enable online editing. It should not have changed for u, but u never know?
 
There are two bits (S:33/11 and /12) that indicate whether online edits are present, but I am not aware of a settable bit that prevents online editing. (but I have still not seen everything !)

I wonder if RSLogix 500 suddenly thinks it is the Starter edition ?

Are the edit buttons simply no longer present, or are they greyed out, or is there some other symptom ?
 
Thanks for all the suggestions. Here's what happened.

I figured out that I rushed out of the program without finishing an edit, to go to another problem elsewhere.

Then when I returned I made offline changes and downloaded the program.

That caused RSLogix to say that I still had Edits Active but I could not accept, test or assemble them because I had downloaded a new revision.

I cured the problem by pulling the battery and shorting VBB to GND and downloading the program into a blank processor.

Problem Solved, thanks.
 

Similar Topics

Hello everyone. Is the PLC CJ1M CPU13 capable of online editing? Or only downloads that will stop the PLC? Thank you.
Replies
3
Views
341
Hi all, Does anyone know if WAGO 750-8100 with e!****pit supports online editing? Thank you.
Replies
0
Views
718
I have been asked to extensively modify a piece of machinery that is very mission critical to the operation, thus not allowed much downtime or...
Replies
4
Views
2,279
In the last two months I have had an issue after making some online changes between the software and an Schneider M221 PLC via ethernet network...
Replies
0
Views
1,088
I was wondering, is possible to remove IO_AIN and replace the instruction with another one without getting offline in RS Logix 5000
Replies
4
Views
1,983
Back
Top Bottom