Communication between PLC5 to Logix plataform via Ethernet
eleall
Jan 2006
Medellín
Greetings
I need to communicate a PLC5/80E to a Compactlogix L35E via Ethernet.
I found in the AB knowledgebase a note that explains how to connect an SLC 500 with a Logix using the MSG block and the PLC 2,5/SLC Mapping in the RSLogix 5000 software. (http://rockwellautomation-es.custhelp.com/app/answers/detail/a_id/19705/kw/Messaging%20from%20a%20SLC%205%2F05%20Controller%20%28channel%201%29%20to%20a%20Logix%20Controller/r_id/113043)
i wonder if this note can be also apllied to a PLC 5, or if there's another way to communicate boths PLCs via Ethernet.
You can do a msg but the plc5 must have a certain firmware revision. I had to upgrade to firmware L1 on a Plc5 20/E. Also I was using an L61 processor but I think an L35E will work too.
Set up a plc5 type tag in the L35E. Then setup a plc5 typed read in the plc5.Setup the multihop out of port 2 and put the IP address of the L35E in.
Hope this helps
The PLC-5E and 1785-ENET "Sidecar" module require firmware that supports "Multi-Hop" messaging, and if you are going to put the MSG instructions in the PLC-5 you will need RSLogix 5 software that supports that function too.
All the examples for SLC-5/05 apply also to PLC-5E (the 5/20E, 5/40E, and 5/80E).
This feature was added more than ten years ago to the PLC-5.
RA Knowledgebase article 19325 has the specifics versions. The firmware revision letter/number depends on the Series letter of the PLC-5.
http://rockwellautomation.custhelp.com/app/answers/detail/a_id/19325
For the PLC-5E controllers, you will need these firmware revisions or newer:
Series F rev A
series E rev D.1
series D rev E.1
series C rev N.1
I have 2 processor on my system micrologic 1100 serie B and PLC5/40E, now i want to send some data from micrologic 1100 to PLC5/40, i have tried...
3,317
plz i need to know if i can add an ethernet model to the cpu 1785-L20B/E (plc5) and if yes, where did i must place it? other thing, i need to know...
1,769
I've got a tough integration question (for me anyway) I have an existing DH+ network. I am installing a new SLC5/05 on an ethernet network that...
3,346
I am having trouble communicating between an existing plc5/20 and a newly installed, in slot 16, basic module. The basic program was copied out...
2,220
HI Any body can help me to get some ideas about how to communicate between two PLC 5/30 processor located about two miles from each other.
2,381