I did remove all dreivers & varibales from Vijeo
Configure PLC as COM1 ,address 1 (Slave),Modbus,19200,8,None, & 1 as stop bits
Define & use %M0 in my logic.(Use is Must)
In HMI add a MODBUS RTU driver(By default it is Master)
Configure HMI as COM2 ,19200,8,None, & 1 as stop bits
Add an equipment as slave address of 1 (same as that of PLC)
Check IEC box.
Add a BOOL varibale addressing t o %M0 in HMI.
Rest every thing was same.Same Cable.
Selector Switch at HMI near COM2 was at RS485 Polar ON.
Things start working.Any one needs any other info ,please ask