I have a Modicon Quantum installed in a large mineral seperation plant, the programing software is concept v2.6. The plant has about 2000 I/O points of which there is about a 50/50 spilt between analog and digital. These are currently all on the modicon 800 series racks as the quantum replaced the 984B. The plant is about 500 m from the plc. The racks are localized in the plant.
We are looking at installing about 100 new analog points and am lookinf at a bus as apposed to installing new racks.
In time we would like to put the existing "multi-parameter, down-loadable, high-level" instruments onto the network as aposed to just getting a 4-20ma signal.
Please give me your informed opinion as to which bus systum would be better suited to my application as discribed.
Hello Murray;
We have worked with Quantum CPUs last year, on a large (13000 + I/O points) distributed control system upgrade for a loading dock. In order to be able to maintain the original TI500 racks, we installed Profibus masters in all the central racks (with Profibus RBCs replacing the TI CPUs). The I/O setup went like a charm, and mapping the Profibus I/O to the Modicon addresses was easy. We also inserted ET-200M racks for newer I/O points over Profibus (both discrete and analog), and used Profibus-PA links to connect temperature, pressure and weight transducers (Siemens and Endress & Hauser)over an intelligent bus. (Using PA and PDM software required a bit more of a learning curve, but the results were very worth while).
All in all, I can't help but recommend Profibus as a distributed system for Modicon PLCs.
Hope this helps,
Daniel Chartier
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
241
I have a backup Processor which is identical to the processor running my plant (140 CPU 652 60). If I load the same project into this backup...
1,503
Hi, Any one know how I can check the status of the Ethernet card NOE77111 status or if there is any communication fault? Thank you!
2,335
Hi, I have new Moodicon PLC CPU 140 652 60 and I want to change the IP address, Subnet mask, and the gateway for this plc using the key pad. The...
4,530
hello, we are using modicon quantum plc and its progrraming software concepr2.2, we have one repeated problem from last many days that our...
2,214