Dear all,
Hope you are well,
I have 1764-24awa module and as you know all inputs are AC.but i have 5 switches operate only 24v what can i do to solve this problem??
 
It's not complicated; this is very simple electric circuitry.

You need relays with 24V coils, and contacts that can handle 120V AC (with extremely low current).

Wire your sensors to the A1 terminal, and wire the A2 terminal to 24V DC Common. That will turn on the relay when your sensor is on.

Wire the common source terminal of the relay to 120V AC hot. Wire the open contact terminal of the relay to the desired input.

Very small relays can be used for these purposes; they are often called "interface" or "interposing" relays. I like the DIN-rail mounted A-B 700H series because they are widely available in my area.
 

Similar Topics

Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
Replies
2
Views
96
Good Day i Have Micrologix 1500 LSP, and I want to get data from plc and send it through Modbus RTU slave; I have only ch0 on that plc I Order...
Replies
6
Views
911
Hello folks, Hope everyone is doing fine. I got an OMRON NS10-TVOOB-V2 hmi screen last day and planning to use it with Micrologix 1500. 1. Is...
Replies
4
Views
1,199
Good morning to all, I need to modify an existing PLC MIcrologix 1500 configured with a Modem on Channel 1 (DF1 Full Duplex) and an...
Replies
7
Views
1,424
Hi to all, Unfortunatelly I can not provide any help with PLC but will do on some other forum for microcontrolers. I need help with PLC to panel...
Replies
10
Views
1,580
Back
Top Bottom