Multiple VFD Enclosure

Beau79AU

Member
Join Date
Feb 2018
Location
NSW
Posts
11
Hi all,

Does anyone know of a calculator for figuring out size of enclosure to house multiple vfd's? We have a job at them moment where we need to house 2 x Schneider ATV650 15kw and 4 x ATV630 2.2kw drives in a single stainless steel enclosure.

Regards,
Beau
 
Hoffman has a calculator to determine what size air conditioner is required for a cabinet housing components with X BTUs for a given cabinet size based on the environment. You could work that backwards.

Start here
 
There is a "Drives Engineering Handbook" published by AB/Rockwell That has this calculation and "rules-of-thumb".
Basically, you calculate the total surface area of the enclosure. You can figure heat dissipation at around 10w/sq.ft. with a 40*F ambient with a 10*F rise inside the enclosure.

They have a graph in the handbook for reference.

CFM requirements = (1.76 x watts)/Temp Rise(*C)
 

Similar Topics

Is it OK to have multiple Frame size VFD's inside the same enclosure that will be dedicated to VFD's only or is there any code/regulations against...
Replies
4
Views
1,728
Hi guys! I have been spending quite a bit of time yesterday and today trying to get a definitive answer to this question regarding protection an...
Replies
10
Views
3,779
Hey guys , I am involved in a equipment installation process wherein the customer wants me to run multiple motors with a single VFD. I...
Replies
3
Views
2,028
Good morning, A Yaskawa A1000 series VFD is controlling a chain at the ref. frequency 1 (let's say 70 Hz) as its default. In winter months, a...
Replies
2
Views
1,298
I have an application in a dairy barn where the customer wants to run his ventialtion fans on a vfd to slow them down and get energy savings. He...
Replies
45
Views
10,173
Back