Jim G.

Member
Join Date
Nov 2007
Location
Georgia
Posts
187
We have a chemical mixing system controlled by Contrologix and display functions by FactoryTalk SE. On one of the process screens there is an actual temperature display and below it is an high temperature alarm setting for a particular grinding mill. The operator has the capability to change the high temperature setting if needed. However, we would like to set a maximum limit that the display will accept. Is this best done in the PLC program or in the FTSE configuration? I am looking for ways this could be done. Thank you for all your help.
 
I like to do both where I need it constrained(or throw an alarm if its out of range, depends on the process). That way the HMI won't let it be setup OOR normally and the PLC will either notify or 'fix' it if it somehow gets set the other way.
 
You just set the values on the min and max entries on the connections tab. Either add the values or link to a PLC tag.

Or more commonly, set it to point to a HMI tag, then you can change the values via an engineering screen.
 

Similar Topics

Hi, Is there an easy way to limit the input tag by using min and max tags from the PLC? Thanks
Replies
1
Views
1,214
Hi Guys, I have got a problem regarding the setting of more than one limit for one input field. I have got four motors for extrusion & One for...
Replies
1
Views
1,664
SELECTED NEW FILE SELECTED PROCESSOR TYPE SELECTED I/O CONFIGURATIONS IM UNABLE TO CONFIGURE MY I/O’S. I HAVE A PAPER COPY OF A PROGRAM AND I...
Replies
0
Views
62
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
Replies
9
Views
224
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
70
Back
Top Bottom