Old August 10th, 2018, 03:33 AM   #1
Nortech
Member
Ireland

Nortech is offline
 
Join Date: Mar 2018
Location: Ireland
Posts: 19
USA low voltage wiring standards (Festo PLC)

Hi All,

I have a project at the moment with a Festo PLC to be sent to the states. It must adhere to UL standards which I am not familiar with. From research I think I should be using Red for 24vdc, Black for 0vdc and white for ground. Is this correct?

Can anyone else offer any advise for US wiring standards?

Thank You.
  Reply With Quote
Old August 10th, 2018, 05:08 AM   #2
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,585
Wiring standards for industrial machinery are covered in a standard called NFPA 79. NFPA is the National Fire Protection Agency, they also publish our National Electric Code (NEC) which is NFPA 70. All of their standards are available at NFPA.org.

But to your question, UL doesn’t care about wire colors so long as you properly identify them, but these color schemes are what you would find in NFPA 79:
DC should be blue,
AC Controls should be red,
AC Line Power should be black,
white is reserved for grounded Neutral
Ground is green or green/yellow.

Last edited by jraef; August 10th, 2018 at 05:10 AM.
  Reply With Quote
Old August 10th, 2018, 06:37 AM   #3
LadderLogic
Member
United States

LadderLogic is offline
 
LadderLogic's Avatar
 
Join Date: Jun 2003
Location: Chicagolandia
Posts: 1,283
Your customer has the ultimate word on this but it is most common to use black for AC circuits 200V and above; red for 120V AC line, white for 120V AC neutral and green for ground.

As far as DC circuits, in many cases it will be brown for DC+ and blue for DC-
__________________
Don't trust, don't fear, don't beg...
  Reply With Quote
Old August 10th, 2018, 06:54 AM   #4
roxusa
Lifetime Supporting Member
United States

roxusa is offline
 
Join Date: Nov 2008
Location: NJ
Posts: 663
I use:
AC Line power :Black
AC Control:Red
AC Grounded Neutral :White
Ground:Green with Yellow Stripe
DC 24+: Brown
DC 0V: White with Blue Stripe (Blue with White Stripe)
DC Control: Blue
__________________
B.Pedersen
if you are going to assume, assume your wrong.
  Reply With Quote
Old August 10th, 2018, 06:58 AM   #5
roxusa
Lifetime Supporting Member
United States

roxusa is offline
 
Join Date: Nov 2008
Location: NJ
Posts: 663
I use Yellow for Live AC Coming from a source that is not disconnected with the Disconnect on the panel ( I have seen Orange used) And must be labeled in Panel. These are typically interlocks from other equipment.
__________________
B.Pedersen
if you are going to assume, assume your wrong.
  Reply With Quote
Old August 10th, 2018, 08:09 AM   #6
saultgeorge
Lifetime Supporting Member
United States

saultgeorge is offline
 
Join Date: Jul 2015
Location: Detroit
Posts: 152
+1 for a different color for interlock circuits plus we add a label, (tag) on the enclosure that will state not all circuits entering/leaving this enclosure are de-energized when disconnecting this panel or something to that effect.
__________________
Detroit City Limit: An Automation Alley Community
  Reply With Quote
Old August 10th, 2018, 05:29 PM   #7
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,253
look up nfpa 79, electrical standard for industrial machinery, and nec 70 - electrical code book, nfpa 70e - arc flash.

there are others, but I don't know your system.

things designed for 50 hz typically burn up in 3-6 months un the USA (personal experience), so get things designed for 50/60 hz.

our electrical outlets are 120 volts ac, not 230 volts.
we also have 220, 440 volts, as well as others, not 380.

I don't know about your location.

james
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC Update - Back Issues Collection Now Available! Phil Melore LIVE PLC Questions And Answers 11 October 22nd, 2015 03:17 AM
Plc inputs/outputs wiring renatusigm LIVE PLC Questions And Answers 23 February 25th, 2012 04:01 PM
Plc suggestion aec LIVE PLC Questions And Answers 36 January 2nd, 2012 01:56 AM
PLC DL05 with encoder signals wiring ALIMARY15 LIVE PLC Questions And Answers 8 September 16th, 2011 07:54 AM
Festo Gear + PLC ----LOST Robinhood LIVE PLC Questions And Answers 3 March 22nd, 2011 11:03 PM


All times are GMT -5. The time now is 10:56 PM.


.