I need to make some changes to two systems. One has a PLC-5/15 and the other has a PLC-5/30.
What cables, interface devices, etc. do I need to connect my laptop computer to these old processors? My laptop has a real serial port, USB, PCMCIA.
 
for the (older/classic) PLC-5/15 you will REQUIRE a DH+ connection ... specifically you can NOT use just a serial-type cable ... note: that handy looking little 9-pin connector on the front will NOT (I repeat NOT) let you use inexpensive RS-232 communications ...

in some cases, it's cheaper to just upgrade the old-style processor than it is to invest in the communication hardware ...

the "text book" answer to your question is:

you need a 1784-PCMK "credit card" for the laptop's PCMCIA port ...

AND ...

a 1784-PCM5 cable to match the PCMK card (be careful with the series A and series B versions - they will NOT interchange) ...

AND ...

a 1784-CP7 adapter ...

do NOT let the supplier talk you into a "modern" 1784-PCM6 cable ... the "good news" is that this one doesn't need the adapter ... the "bad news" is that you won't be able to remove the adapter to plug into the 9-pin port on the front of your classic PLC-5/15 ... specifically, the classic processors don't have the little round 8-pin miniDIN connector featured on the PCM6 cable ...

in the past you could get all of the above listed parts as a kit ... ask for part number 1784-PCMC if it's still available ... the last time I checked (years ago) the price was about US$1,500.00 ...

so ... once you've got the older PLC-5/15 covered (as listed above), you can use the same cable to connect to the new models too ...

or – if you ONLY need to communicate with the new model, then all you really need is a simple RS-232 cable ... 9-pin-female on one end to a 25-pin male on the other end ... the official part number is 1784-CP10 but you can build your own if you like ... we'll look up the pinout if you're interested ...

possible exception: sometimes the processor's RS-232 port has been reconfigured for use as a "barcode reader" port or something along those lines ... if so, you'll have a hard time trying to program through it ... let us know if that's your problem ...
 
Last edited:
Thanks, Ron

My AB supplier quoted a
1784U2DHP USB to DH+ interface to replace the
1784-PCMK or 1784-PCMC. The cable and adapter are still good partnumbers. Total price is $2295 Canadian.

 
Thanks, Ron

My AB supplier quoted a
1784U2DHP USB to DH+ interface to replace the
1784-PCMK or 1784-PCMC. The cable and adapter are still good partnumbers. Total price is $2295 Canadian.


See picture below from the 1784-U2DHP manual. Double check this with your AB supplier.

Cable.jpg
 
Last edited:
in some cases, it's cheaper to just upgrade the old-style processor than it is to invest in the communication hardware ...

I second Ron on this - it is the route I took when encountering a 5/15. I have the PCMK card but the customer did not. It was cheaper to change the processor than buy the PCMK card.
 
I just did a quick search for "PLC-5" on E-Bay and found a lot of options ...

here's one that caught my eye based on what you've posted so far ...

http://cgi.ebay.com/Nice-ALLEN-BRAD...tZBI_Control_Systems_PLCs?hash=item588663dce9

current bid is about $99.00 ... or "buy it now" for about $199.00 ...

also notice that most of the PLC-5/15 processors are going for about $50.00 each ...

disclosure/disclaimer: I have ZERO connection with - or knowledge of - the seller linked above ... this is for example only ...

incidentally, in most cases you should be able to just "download" the existing PLC-5/15 program to any larger/newer PLC-5/XX processor ...

please let us know how this project works out for you ... this is a fairly common question on the forum ...
 

Similar Topics

I am using Mitsubishi PLC :FX3g and downloaded the program in it. When I connect Mitsubihi FX2N-4DA expansion module, it lost its communication...
Replies
3
Views
243
Hi, The VersaMax PLC suddenly stop running (no LED on run function) so I'm trying to upload the program. The HMI connected to it says "Host...
Replies
0
Views
117
hi hello every one . i have a Omron nt31c hmi and i want to connect with ls plc XBC DR60SU via rs232 . do any one now how ?? secondly :i have...
Replies
1
Views
184
I'm trying to establish communication between an HMI DELTA (DOP-B07E515) and a PLC IDEC (FC6A-D16R1CEE) via the RS-232C/485 module (FC6A-SIF-52)...
Replies
2
Views
500
Sorry for the basic question: At the moment, the PLC [S7-1200] is connected to a laptop (contains TIA Portal) via the ethernet port. When I add...
Replies
10
Views
1,425
Back
Top Bottom