DeviceNet Fiber Optic
I am not being very clear- I want to know if I can go from
a devicenet scanner card to devicenet I/O with fiber optic cable.
THANKS
If data exchange were the only requirment than I could possibly see this as a possiblity. But, I believe that devicenet devices are powered off of the devicenet communication cable. correct me if I am wrong.
With Siemens I can use a fiber optic master with fiber optic slaves
and power the slave devices with 24vdc. The cable is for communication
only. I was trying to do the same using devicenet. I wonder what is needed to program the PLC using devicenet then,it must be a special
adapter.
JRW-
DeviceNet, being a CAN-based specification, doesn't have a native fiber version. However, check at:
www.ccontrols.com/pdf/eadn.pdf
This is a DeviceNet extender. Each extender manages it's own sub-network and extenders are linked via fiber optic cable or BNC connectors to form a network backbone.
I've never used one of these. I stumbled across it with an Internet search.
As an aside, most DeviceNet I/O adapters (as opposed to discrete devices with DeviceNet built in) use a 5-terminal wiring connector to terminate the DeviceNet cable. While the DeviceNet adapters need power from somewhere it does not have to come from the DeviceNet cable. It can come from any appropriate power source you choose.
Hope this helps
Keith
I've used Western Reserve Controls (www.wrcakron.com) DeviceNet/Fiber Optic converter successfully; it's a store-and-forward repeater and you need two per link.
DeviceNet, as you've found, really doesn't have a "fiber optic option" the way Profibus or Ethernet do. DNet was designed to be cheap to wire and run power to, and fiber is neither of those.
Omron have wireless Device Net. Don,t know the price yet as the devices have not been approved in Australia yet. Our authorities have to be as slow as a wet week in approving these things. If the price is OK, it may be a solution for you.
I had a look at the ccontrols devices and found them far too expensive. Also, you cannot "loop in - loop out" connect them - only 2 per Device Net network. Have not looked at the other ones mentioned in one reply - going looking now.
beerchug
Just been there - PRICEY. Have already forgotten about them. Cheaper to use more PLC's and Ethernet.
We've run into an old system that we are upgrading which is still running Steeplechase with Citect using Devicenet to Wago. I had some experience...
142
Sigh, DeviceNet noob... I have a 1756-L55, with a DeviceNet module, and 10 PF700 all commanded with DeviceNet. One of the PF700's blew up...
129
Good day Forum Members I got a older Lincoln welder and hoping to make it work at our shop. Welder in question is the Lincoln Power Wave 455M...
197
Hello Friends We have 10 Powerfocus 4000 with DeviceNet, We need to backup the configuration, the Powerfocus is detected but as unrecognized...
104
Hello, I have a device with 68 words input. But one block on the Devicenet Scanner is only 61 words. I am trying to map this device to 2...
526
