Transfering using WinCC flexable

Join Date
Feb 2004
Posts
84
Hi all,

I am using WinCC flexable v.2008 Sp2 and transfering project to a MP377 12" Touch HMI via mode ethernet / IP address. My issue is that I had downloaded or (Transfered) to 3 different HMI's fine with different IP's on the 4th HMI I had changed IP address and hit apply just like the last 3 but this time it transfered to the last HMI I have done. I checked and double checked to make sure IP's had accepted the change after hitting "Apply" and it did but no matter what IP I changed it to it still went to the same HMI. Has anyone had this happen to them or any ideas of what to look for? I tried a different Assbly line the following day and it downloaded the first HMI fine but when changed addresses it had done the same and would only go to the last HMI downloaded to. Any help would be appreciated.
 
You also change the IP setting in "Communication/connections"?
For the integrate wincc to S7 project, you may need to change setting in HW Config.
 
1. Be sure to set the IP on the Panel by the Windows Control Panel.
2. Ping the panel from your PC. Most go OK.
3. Disconnect the panel from ethernet, and ping again. Must fail.
4. When you transfer from Flexible, you can manually set the IP of the device. Check that you use the correct IP.
5. If still not OK, transfer locally with only your PC and Panel connected by ethernet, and nothing else connected.

If still not OK, post some screnshots of the transfer dialog from Flexible.

NB. The HW Config settings for the panel are not directly related to the transfer settings when using ethernet.
 

Similar Topics

AB 1200P 6181P Needing to transfer .cli file from one 1200P to another. I've loaded the file to the new one but it will not open. File name is KM...
Replies
0
Views
1,217
Hi guys. I am using RS Studio v24 and I have a structure BOOL[2048] inside. When I give project to our HMI designer he sees that array of bools...
Replies
6
Views
2,158
Hi, I've been trying to run my project in Simulation (and check display on VNC viewer). When I try to download a procjet to simulator, then I...
Replies
2
Views
1,498
Hi All, I've recently gained control of an existing control system used for purifying water. We have an SLC 5/05 processor and are using RSView...
Replies
8
Views
2,973
Everyone, So I have been on this forum for the last 24hours straight. I have learned a ton, like always. Yesterday I posted about resetting all...
Replies
1
Views
2,673
Back
Top Bottom