Question Current Transducer

I was trying to attach a pic but for some reason it wont let me. Anyways i zipped it and attached it.

My question is regarding the grouding of terminal 3. I was curious as to why that is done. From what i can tell its for reference, but correct me if i am wrong. Could someone give a better explanation if there is to why that is done.
Attached Files
File Type: zip CT.zip (82.9 KB, 20 views)
  Reply With Quote
Old January 26th, 2007, 02:41 AM   #2
Ken Moore
Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: Upstate South Carolina
Posts: 2,346
I posted your pic for you.

__________________
"To give real service you must add something that cannot be bought or measured with money; and that is sincerity and integrity."
- Donald A. Adams

  Reply With Quote
Old January 26th, 2007, 04:45 AM   #3
Sparkz
Member
Belgium

Sparkz is offline
 
Sparkz's Avatar
 
Join Date: Mar 2006
Location: Tessenderlo
Posts: 250
This relates to grounding transformers...

EN60204 states that the secondary windings of any transformer (so including current transformers, like the CT in the drawing) have to be grounded for safety reasons.

Edit: If it's the first time you've come across CT's, please be extremely careful as to shortcircuit the secondary before disconnecting the CT from the circuit. Or make sure there's absolutely no line current flowing through it when disconnecting.

Last edited by Sparkz; January 26th, 2007 at 04:53 AM.
  Reply With Quote
Old January 26th, 2007, 05:44 AM   #4
Andybr
Member
United Kingdom

Andybr is offline
 
Join Date: Oct 2004
Posts: 587
Expanding on Sparkz closing comment you should still shortcircuit the CT secondary before disconnecting it even if you are absolutely sure there is no current flowing. Just because there is no current when you disconnect it does not follow that the circuit will not be re-energised. The open circuit secondary voltage on a CT can be extremely high and is quite capable of causing injury or damage.
Andybr
  Reply With Quote
Old January 26th, 2007, 07:59 AM   #5
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,906
The output voltage of a CT with an open lead is the ration of the CT to the line voltage. So, if you have a 500:5 CT on a 480 volt line the potential is 4,800 volts.

From personal experience, that represents a significant shock hazard!
  Reply With Quote
Old January 26th, 2007, 10:39 AM   #6
Sparkz
Member
Belgium

Sparkz is offline
 
Sparkz's Avatar
 
Join Date: Mar 2006
Location: Tessenderlo
Posts: 250
Sorry Tom, but I was told that a current transformer will raise its secondary voltage to ANY level, just to get the correct current flow through its secondary, that is, according to its ratio. That's why CT's are supposed to be shorted when not connected to an ampmeter or the device (kWh meter?) mentioned above.

It would also explain why CT's with a 20:5 ratio burn when the secondary is left open. Leaving the secondary open is not only hazardous to personel, but it will definitely destroy the CT. I've seen CT's like this burn out in a matter of seconds on a 230V generator, just by leaving the clamps open, so the line voltage doesn't really matter.
  Reply With Quote
Old January 26th, 2007, 11:06 AM   #7
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 6,147
Eureka! Ya' never know what you're gonna to find here...

I've been purchasing power transducers from one supplier that we are very happy with, but they don't offer quite what I need in a multi-variable transducer for one particular application. So I googled the part numbers off the picture to find out who made the OP's instrument and gave them a call. Crompton has something that might just be the ticket.
  Reply With Quote
Old January 26th, 2007, 11:20 AM   #8
Andybr
Member
United Kingdom

Andybr is offline
 
Join Date: Oct 2004
Posts: 587
Alaric.

I have used many Crompton transducers in the past and they are perfectly OK but have you considered using an Energy Meter with some kind of serial/network connection. I currently use Merlin Gerin PM710MG meters (also available as Square D) on Modbus and they provide all of the information you would normally require (including TDH). I have used other similar instruments including some made by PML which are equally good but the MG units are comparable in price to a KW transducer alone.
Andybr
  Reply With Quote
Old January 26th, 2007, 01:37 PM   #9
Gerry M
Member
United States

Gerry M is offline
 
Gerry M's Avatar
 
Join Date: Jun 2004
Location: Auburn, NY
Posts: 255
Quote:
Sorry Tom, but I was told that a current transformer will raise its secondary voltage to ANY level
I believe Tom is correct, except it should be 48,000 Volts(480*500/5). That definitely is a hell of a significant shock hazard. I know in theory the voltage can go to infinity, but that isn't the reality based on many factors, such as internal coil resistance and core saturation, etc. Either way its not good not to short.

Last edited by Gerry M; January 26th, 2007 at 01:53 PM.
  Reply With Quote
Old January 26th, 2007, 03:14 PM   #10
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,906
Quote:
Originally Posted by Gerry M
I believe Tom is correct, except it should be 48,000 Volts(480*500/5). That definitely is a hell of a significant shock hazard. I know in theory the voltage can go to infinity, but that isn't the reality based on many factors, such as internal coil resistance and core saturation, etc. Either way its not good not to short.
You are absolutely correct, Gerry - my math was off by an order of magnitude!
  Reply With Quote
Old January 26th, 2007, 03:22 PM   #11
rajy2r
Member
Canada

rajy2r is offline
 
rajy2r's Avatar
 
Join Date: Nov 2006
Location: Vancouver
Posts: 117
Thx. for the help guys. Appreciate it.
  Reply With Quote
Old January 27th, 2007, 08:50 AM   #12
Sparkz
Member
Belgium

Sparkz is offline
 
Sparkz's Avatar
 
Join Date: Mar 2006
Location: Tessenderlo
Posts: 250
Hi Tom & Gerry (?!),

The line voltage is totally inherent to a current transformer! The AC line voltage can have any value from 0V to 1000V (some types even more), as long as the current passing through the CT does not exceed its ratio.

Sorry, but I can't see the relation between the line voltage and the open clamp voltage of the CT.
  Reply With Quote
Old January 29th, 2007, 02:46 AM   #13
Sparkz
Member
Belgium

Sparkz is offline
 
Sparkz's Avatar
 
Join Date: Mar 2006
Location: Tessenderlo
Posts: 250
Oops, in stead of 'inherent' I meant 'independent'.
  Reply With Quote
Old January 29th, 2007, 07:48 AM   #14
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,906
The voltage of the lline defines the potential energy the CT has available to push current across the opent circuit. This relationship can be found in some of hte CT manufactuer's literature.
  Reply With Quote
Old August 14th, 2007, 07:58 PM   #15
arroyo
Member
United States

arroyo is offline
 
Join Date: Aug 2007
Location: New Jersy
Posts: 1
I'm looking for the correct size CT (current transformer)
I want to install (1) CT to monitor the amps of one leg of a 3 phase 460 volt 125 HP motor with a full load amps of 167. I have an analog ampmeter scaled from 0 - 150 amp, and a CT with a 300 to 5 ratio. , please advice if this will work, or do I need to make some changes.
thank you for your help

Last edited by arroyo; August 14th, 2007 at 08:00 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
OT: VFD Marketing BS dash LIVE PLC Questions And Answers 18 December 17th, 2006 06:51 AM
motor alternating directsoft 32 on a DL06 DRThorne LIVE PLC Questions And Answers 15 November 9th, 2006 08:05 PM
Current transducer shabi LIVE PLC Questions And Answers 7 November 12th, 2005 07:27 AM
3 Phase Current sparky64 LIVE PLC Questions And Answers 6 September 9th, 2004 09:30 AM
On the subject of inrush current Steve Bailey LIVE PLC Questions And Answers 24 September 1st, 2003 06:19 PM


All times are GMT -5. The time now is 03:19 PM.


.