plc5 message number reset fault

michaelchan

Member
Join Date
Jun 2007
Location
FUJIAN PROVINCE
Posts
43
plc5 talk to HMI(hitech in taiwan),use preset message display in HMI,when bit in PLC is set 0,relative message could not be rest,for example:

b10:7/12 value is 1,relative message number(n11:9 in my pro)is 124,so HMI will display 124th message,but now when b10:7/12 is 0,n11:9 value is still 124,so confused about it...

attached is pro,hope someone can catch me and give me a hand.

Thanks.
 
do a seach in you plc 5 program for n11:9 there should be move instructions moving in those numbers into n11:9. your HMI is just reading the number that is put into n11:9. take a look at your data in n11:9 when there is no message in you display and that should be the number you can move into n11:9 when b10:7/12 isn't true.
 

Similar Topics

Hello, is it possible to read a message using a controllogix L61, from a SLC, that is connected to a PLC-5 that already is sending data to the...
Replies
7
Views
2,143
Hey everyone! I am trying to set up some messaging between two of our older PLC's, having difficulty getting the configuration nailed. I've made...
Replies
2
Views
1,270
When creating a new input on a remote microLogix transmitting to the PLC5 via 9810 MDS Data Interface on Channel 0. Will the data file...
Replies
1
Views
1,409
I have a slc5/05 writing to a plc5/40 processor ( using message), everythings works ok for hours sometimes days then it gives error 37 and stops...
Replies
8
Views
3,466
I'm trying to use a message instruction to read the value from a PLC5/20 into another. I have searched the forum, but am getting more confused...
Replies
1
Views
2,130
Back
Top Bottom