RSLogix 5000

I figured out the timer PCE errors for the acc. and pre. Any idea on the status bit conversion to gsv. Any help is appreciated. Thanks
 
Details ! The PLC-5 Status file is dozens of words long, and the GSV instruction has dozens of different objects it can access.
 
For example S:7/8 labeled as processor status rack 0 BT queue full. How would I convert that to a GSV. I don't understand the structure and terminology of that instruction.
.
 
That's a Status bit that doesn't have an equivalent in ControlLogix.

There isn't a built-in queue for MSG instructions (which are what provide the Block Transfer function in ControlLogix), so I would either not use the status bit at all, or provide an alternative method of detecting and displaying problems with the ControlNet data transfer to and from analog or specialty modules.
 

Similar Topics

Hello all, I have a question in regards to RSlogix 5000. I am having issues with the program force closing when I try to make online edits. We...
Replies
0
Views
95
Greetings ... someone sent me a request for some student handsouts that I developed ... turns out that I had this hosted on my business website...
Replies
0
Views
109
Thank you for any and all responses/help. I have an RSLogix 5000 v20 and a Cognex In-Sight v5.9 spreadsheet (8502P). I can not figure out how to...
Replies
0
Views
101
Hi All, I've been pulling my hair out trying to fix this for a few days and need some advice. I have V19.01, v20.05, V21, V24, V30, V31, V32...
Replies
5
Views
351
Hello Friends I have a installation with v16, v17, v18, v19, v20. When I tried to open a v20 file, the enable source protection was not enabled...
Replies
1
Views
214
Back
Top Bottom