I am about to swap the computer and software that has been communicating to a Micrologix 1500. We’re going from Serial/Serial to Serial/USB and a newer version of software.

Other than the USB to serial driver and checking the normal COM port settings on the PC side, is there anything else to check to make sure communication is established with no issues?

Anything with the PLC that needs to be checked or reset?
 
If you have the opportunity, check to make sure the MicroLogix serial port is set for DF1 Full Duplex protocol, which is the default.

In the very unlikely chance that your PC/PLC connection use DH485 protocol, it won't work through a general-purpose USB/Serial converter and will require a 1747-UIC or equivalent.

But it's far more likely that you'll just set the software to work with the correct COMx serial port in Windows, and the new connection will work fine.
 

Similar Topics

Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
219
Hi all, I am having an issue where some of my HMI push Buttons and Indicators go in to error when I navigate to a new screen. I am using a...
Replies
16
Views
421
We have a new machine that uses an armor block to transfer input signals for conveyor position that continuously alarms out on no position change...
Replies
0
Views
83
Hello everyone, I am trying to change the IP address of the Omron PLC (NJ30-1200) and HMI (NB7W-TW01B) to fetch the network on our network...
Replies
7
Views
278
Dear Experts, I'm just started working with GEO SCADA and I need your valuable help. Currently, I'm trying to edit the alarm limits on MIMIC...
Replies
0
Views
206
Back
Top Bottom