Communication between S5 and rslogix 5000

You would need the following to configure the S5 side:

IM308-C Profibus-DP module (6ES5-308-3UC21)
Flash EPROM (6ES5-374-1KH21)
In S5-115U racks, an adapter casing (6ES5491-0LB11)
COM Profibus V5.1 software
USB Prommer (or Siemens PG with Prom burner)
Profibus cable and connectors for the PLC to PLC connection.

The USB Prommer or Siemens PG is required to write to the FLASH Memory card for the IM308C, which you configure with COM Profibus.

Make sure you have enough unused I/O (P) area to handle the amount of information you need to exchange. If you need a larger amount of information, it is better to make the IM308C be the Profibus-DP master, and get a Controllogix Profibus-DP slave module. With the IM308C as the master, it is possible to exchange up to 400 bytes of total information with the Prosoft Profibus DP slave module (max. 244 bytes input and max. 244 bytes output, but the total not more than 400 bytes).... and it is possible to read/write the data without using I/O memory areas in the S5.
 
Last edited:

Similar Topics

Hi guys I´m looking for your help. I need to Set up a communication between Vijeo Designer and RSlogix 500, but I don´t know how. I found that I...
Replies
10
Views
5,320
I have a few inputs going into this festo I/O module. How do I go about setting up this module to communicate with with the 5/05 PLC ? I've made...
Replies
6
Views
3,540
Hi all, I am having RsEmulator ver16 and FT view SE ver6. I want do develope communication between them remotely i.e. On laptop I will run Logix...
Replies
3
Views
6,005
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
Replies
0
Views
17
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
Replies
4
Views
72
Back
Top Bottom