Event_In Contact_in _____________
-----] [------+--------]/[--------[TON DN]-----+-----
[COLOR=blue]|[/COLOR] [Name the_ton] [COLOR=Blue]|[/COLOR]
[COLOR=blue]|[/COLOR] [PRE 10000] [COLOR=blue]|[/COLOR]
[COLOR=blue]|[/COLOR] [Acc 0] [COLOR=blue]|[/COLOR]
[COLOR=blue]|[/COLOR] ------------- [COLOR=blue]|[/COLOR]
[COLOR=blue]|[/COLOR] [B][COLOR=blue]Contact_Out [/COLOR][/B][COLOR=blue]|[/COLOR]
[B][COLOR=blue]+--------( )----------------------------+[/COLOR][/B]
the_ton.DN [COLOR=Blue][B]Alarm_Reset_In[/B][/COLOR] Alarm_Out
----+-----] [-------+---[COLOR=blue][B]------]/[-----[/B][/COLOR]-------( )--------
[COLOR=blue][B]| |[/B][/COLOR]
[COLOR=blue][B]| Alarm_Out |
+-----] [-------+[/B][/COLOR]
-----] [---------------]/[--------[TON DN]-----------
[Name the_ton]
[PRE 10000]
[Acc 0]
the_ton.DN Alarm_Out
Event_In Contact_In _____________
[COLOR=blue][B]| Alarm_Out [/B][/COLOR][COLOR=blue][B][COLOR=Blue][B]Alarm_Reset_In[/B][/COLOR] |
+-----] [------------]/[---------+[/B][/COLOR]
I thought some more about this, and my previous post #4 may have the reset logic in the wrong place, as it allows the operator to suppress the alarm by laying a wrench on the reset button.
Corrected logic is below.
Behavior
- If The_Coil does not close before time (T+10000ms), then there will be an alarm.
- The alarm is triggered by the PLC output Alarm_Out changing from 0 to 1
- If there is an alarm, it will not clear until Alarm_Reset_Button is pressed, after either The_Coil closes or Event_In becomes 0.
External devices
- Alarm_Reset_Button
- Momentary button to reset alarm after either Event becomes 0 or The_Coil closes (Contact_In becomes 1).
Code:Event_In Contact_In _____________ -----] [------+--------]/[--------[TON DN]-----+----- [COLOR=blue]|[/COLOR] [Name the_ton] [COLOR=Blue]|[/COLOR] [COLOR=blue]|[/COLOR] [PRE 10000] [COLOR=blue]|[/COLOR] [COLOR=blue]|[/COLOR] [Acc 0] [COLOR=blue]|[/COLOR] [COLOR=blue]|[/COLOR] ------------- [COLOR=blue]|[/COLOR] [COLOR=blue]|[/COLOR] [B][COLOR=blue]Contact_Out [/COLOR][/B][COLOR=blue]|[/COLOR] [B][COLOR=blue]+--------( )----------------------------+[/COLOR][/B] the_ton.DN Alarm_Out ----+-----] [------------------------+-----( )-------- [COLOR=blue][B]| |[/B][/COLOR] [COLOR=blue][B]| Alarm_Out [/B][/COLOR][COLOR=blue][B][COLOR=Blue][B]Alarm_Reset_In[/B][/COLOR] | +-----] [------------]/[---------+[/B][/COLOR]
Both versions work, so nothing "wrong", although the first version would prevent the alarm if the reset is held, while the second version will allow the alarm even if the reset is held. (Held could be a short, broken button contacts, etc). All a matter of preference or requirement.
This is probably more than the OP asks for; remove the blue code sections for the bare minimum.
Behavior
- An Event occurs at time T
- If The_Coil closes before time (T+10000ms), then there will be no alarm
- If there is an alarm, it will not clear until Alarm_Reset_Button is pressed, even if The_Coil closes.
External devices
- Event
- Physical contact that initiates the process
- The_Coil
- Physical relay that must close within 10000ms of contact Event
- Coil_feedback
- Physical contact feedback on The_Coil, that closes when The_Coil closes
PLC Inputs
- Event_In
- NO: input that detects (becomes 1 on) closure of contact Event
- Alarm_Reset_In
- NO: input that detects (becomes 1 on) closure of contact Alarm_Reset_Button
- Contact_in
- NO: input from Coil_feedback that detects (becomes 1 on) closure of The_Coil
- N.B. this is related to, but separate from, Contact_Out
PLC Outputs
- Contact_Out
- Output to drive The_Coil, which The_Coil should close] within 10000ms after Event_In becomes 1
- This output, and the blue branch below, are not necessary if external device Event is physically wired to close The_Coil, external to the PLC
- Alarm_Out
- Output to alarm if input Contact_In does not become 1 (indicating that The_Coil has not closed) within 10000ms after Event_In becomes 1
Sections in blue are optional and extra bells and whistles:
Minimal case:Code:Event_In Contact_in _____________ -----] [------+--------]/[--------[TON DN]-----+----- [COLOR=blue]|[/COLOR] [Name the_ton] [COLOR=Blue]|[/COLOR] [COLOR=blue]|[/COLOR] [PRE 10000] [COLOR=blue]|[/COLOR] [COLOR=blue]|[/COLOR] [Acc 0] [COLOR=blue]|[/COLOR] [COLOR=blue]|[/COLOR] ------------- [COLOR=blue]|[/COLOR] [COLOR=blue]|[/COLOR] [B][COLOR=blue]Contact_Out [/COLOR][/B][COLOR=blue]|[/COLOR] [B][COLOR=blue]+--------( )----------------------------+[/COLOR][/B] the_ton.DN [COLOR=Blue][B]Alarm_Reset_In[/B][/COLOR] Alarm_Out ----+-----] [-------+---[COLOR=blue][B]------]/[-----[/B][/COLOR]-------( )-------- [COLOR=blue][B]| |[/B][/COLOR] [COLOR=blue][B]| Alarm_Out | +-----] [-------+[/B][/COLOR]
N.B. this assumes Event is wired directly to The_Coil
N.B. in this case, when Event_In is 1 and an alarm has been triggered, that alarm will stop if the The_Coil closes.
Code:Event_In Contact_in _____________ -----] [---------------]/[--------[TON DN]----------- [Name the_ton] [PRE 10000] [Acc 0] ------------- the_ton.DN Alarm_Out ----------] [------------------( )--------
Drbitboy, I think the second Program is much user friendly. It work perfectly on the simulator but, but a reset button between ton. DN and Alarm out will make it even better
A momentary button, between [the_ton.DN] and [Alarm_Out], that needs to be pressed and held is not a reset button; it is a [temporary silence/disable alarm]. That's why I improved the code from post #4 to post #5. This may be acceptable, or even necessary if a audible alarm needs to be temporarily silenced.
And a push (or toggle or maintain) button, that stays in once pressed, is also not a reset button; it is an [alarm disable] i.e. it disables the current and all future alarms. This is probably not a good idea; if an audible alarm needs to be silenced then there should be a separate rung, with temporary* logic, for the audible alarm but the HMI alarm should remain.
The way the second set of rungs are written, the alarm is only reset when either
* "temporary" means it stops the audible alarm for the current alarm, but the audible alarm would be re-enabled for the next such event.
- the delayed The_Coil finally closes and [Contact_In] becomes 1,
- OR
- the trigger event ends and [Event_In] becomes 0.
Drbitboy, the problem with the post #5 is the alarm the alarm is still energized with the Alarm _Reset _In open. As long as the _TON _DN is set , the alarm will still be audible even if Akarm_Reset_In is open.
Have you done the simulation, I tried and that's a problem
That is intentional: there is a difference between alarm reset and alarm disable. If it can be disabled, what is the point of having an alarm?
An alternative would be to call it an Alarm Acknowledge, so the operators must acknowledge that there was an alarm condition. It depends on the severity of the condition, i.e. is it important to know that it happened?
....I concur
Different ways of going about acknowledging the alarm , it depends on the application.
Sorry for the late feedback after the initial post; I have been busy all week. I work 12 hours daily from 6am - 6pm at an oil mill as an industrial Electrician, very little free time at my disposal