Star Connected Motor Speed Controlling Using Drives

aju

Member
Join Date
Jan 2005
Posts
22
Hello Every Body
I Have A Telemecanique Drive For Controlling Speed Of 1.5 Hp Rating Motor. Motor Winding Is Star Connected. After Discussion We Found That We Have To Change The Star Connected Motor To Delta Connection
Can Anybody Suggest Easy Suitable Solution.

Regards

Ajju
 
There is not enough information in this question. what voltage is the motor is it 400V star and 230V delta? or 230V star?
What model drive is it?
Is the drive a 230V 1 phase in and 3 phase out or 400V 3 phase.
 
Going from a star connected motor to a delta connection on the same motor will normally result in the motor voltage rating going down and its current rating going up.

Why would you want to do this? More info please.
 
The motor is 400V star and 400V IN and 3 phase out.for controlling the speed of roller.
 
What is the part number of the Telemecanique drive?

If the drive is a 230V drive then you can connect the motor in delta OK. This is usually used when you have a 1 phase 230V supply and you want to drive a 3 phase motor that us 400V star or 230V delta connected.
 
aju, please give us the input voltage rating of the VFD. Also, conversion of a small motor from star to delta is only possible if you have all 12 leads available (dual voltage) or six leads if single voltage.

If the motor is star connected internally (nine lead for dual voltage, three leads for single voltage), it probably is not practical to reconfigure the motor.
 

Similar Topics

Here's a question I thought I'd never ask with all my 50 years of experience but I don't know - so I'm asking. I have to change a star delta...
Replies
23
Views
3,148
Hello PLCs.Net! We have 3 elements in a star configuration, and each of the elements are rated for 20kW 120V - This is all I know about the...
Replies
1
Views
1,275
Hello Everyone, I have a few questions regarding the start of a motor The nameplate of the motor is 380/660 delta/triangle 15.1/8.7A The...
Replies
42
Views
12,178
Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
Replies
6
Views
2,617
kollmorgen servostar 400 x7 port support both can and profibus How to connect with this module through profibus instead of can ?📚
Replies
2
Views
1,565
Back
Top Bottom