I'm not exactly clear how forcing works on Logix, 1756-L73. I did some Googling but the information seems to relate only to forcing physical outputs.

We had a belt today we needed to start, but various interlocks kept it from running. I don't understand PlantPAx yet, but I believe we had everything bypassed. From the HMI there is check-boxes to actually allow the interlock to be bypassed, and another set to actually bypass.

On the PLC, there is function block diagrams for the motor. I can see for the PF525 addon profile the Intlk_IntlkOK was 0 but I couldn't figure out how to force it to 1.

TL;DR I don't understand how to force controller tags. It wouldn't let me modify the Force Mask (i/o forcing was enabled).
 
You don't have something set up correctly with the bypass function.

From the interlock faceplate:
Verify that the "Can Bypass" is checked in the engineering tab
Verify that the "enable bypass" is check in the maintenance tab

In the PLC verify that the PF525.Sts_BypActive is wired to the PF525_Intlk.Inp_BypActive.


The interlock faceplate will tell you which interlock input is holding you out.
 
Last edited:
Ok, this gives me something to look for next time...
I know we had all of the Can Bypass and Enable Bypass checked true.

I do see a wired connection between BypActive and Inp_BypActive, should the tag actually be Sts_BypActive? Maybe it is not linked properly? My communications went down to the plc a few minutes ago so I can't verify that..
 
Ok, this gives me something to look for next time...
I know we had all of the Can Bypass and Enable Bypass checked true.

I do see a wired connection between BypActive and Inp_BypActive, should the tag actually be Sts_BypActive? Maybe it is not linked properly? My communications went down to the plc a few minutes ago so I can't verify that..

I'm not sure what the difference between them are. The Intlk manual shows using the sts_BypActive so thats what Ive always used.
 
I'm not sure what the difference between them are. The Intlk manual shows using the sts_BypActive so thats what Ive always used.

I've looked into other equipment, which is configured the same way and working. I believe all the interlocks were properly bypassed in the PlantPAx object because the state of Sts_BypActive and Sts_NBIntlkOK were both 1.

However Sts_IntlkOK was not 0. I haven't figured out yet why that is. I know a safety relay was jumpered to eliminate F059 at the vfd.

So, is there no way for me to force these tags from Logix? I was considering doing a live edit and wiring in a '1' value tag, but opted not to. There has to be a simpler way I'm missing.
 

Similar Topics

Dear Fellows; I am working on a very old machine which is designed in GE 90-30 PLC system. I have some difficulties like 1. How a force to...
Replies
3
Views
298
Hi. This is the first time I do a project with Rockwell PLC from scratch. I started a bit just building some AOI for a couple things I need to...
Replies
2
Views
532
Hello, when trying to force two outputs nothing happened. The text ON appeared by the adress. It was also possible to force off, which also...
Replies
17
Views
4,740
In GX developer, is there a way of forcing a digital input to ON (e.g. X070 to TRUE/On). I've just installed a QX10 module and I want to check...
Replies
15
Views
4,841
Hello, Controllogix 5572 with Studio 5000 v33 and FactoryTalk View SE v12. Is there a way to force I/O bits using HMI pushbuttons? I've tried...
Replies
6
Views
2,824
Back
Top Bottom