Vijeo, Majelis disk full issue

bogu

Lifetime Supporting Member
Join Date
Mar 2020
Location
Alberta
Posts
22
Greetings,
This just started today - download issues with the Majelis and Vijeo. Its a small program and I don't understand where the issue is? How can the memory be full? If so, can I clear it?

  • I've confirmed the runtime is good (6.2.9.36).
  • Magelis (GTO4310) date of manufacture is recent.
  • Memory capacity is more than adequate.

Thoughts?

Code:
------------------------------ Download ------------------------------

---------------------- Checking Connection ----------------------

[XXX_HMI] Connection Confirmed
--------------------------------- Validating ---------------------------------
Validating Services
Target - XXX_HMI
XXX_HMI - HMI
Warning 2131: Enable Download Security to reduce unauthorized access to the target machine.
XXX_HMI - I/O
SRAM - Total: 512 KB, Used: 78 KB, Available: 434 KB
Validation Complete - 1 Warning(s)
---------------------------- Generating Code ----------------------------
---------------------------------- Compiling ---------------------------------
--------------------------------- Romizing ----------------------------------
Calling romizer
Romizer successful
HMI: Project 514 KB, System 40,885 KB, Total Size 41,399 KB (42,392,064 bytes).
Web Gate: Project 58 KB, System 1,004 KB, Total size 1,062 KB (1,087,488 bytes).
------------------------------- Downloading -------------------------------

Downloading XXX_HMI...
Processing Web Gate...
Processing runtime...
Processing project...
Sending files...
Error 1830: [Target] [XXX_HMI] unable to continue download.  Disk may be full.

  Downloading Failed - 1 Error(s), 1 Warning(s)
Best regards,
 
Last edited:
Vijeo, Magelis disk full issue

Bah - got it figured.
(Sorry I misspelled Magelis / Majelis)

I had to reformat the SD card? I've been using this same card for months.... made sure it was FAT32 and picked a cluster size of 1024 as its mostly small files.

All good now. :unsure:

Cheers -
 

Similar Topics

Good Day all. I am currently busy with a schneider HMI design in vijeo designer and i want to know how you can animate an image to move on the x...
Replies
2
Views
155
Hello, I have been tasked with adding some analog signals for display and alarm setup in some old Schneider Electric HMIGTO HMI-panels. I have...
Replies
4
Views
177
My system are taking data from RHT sensors, around 45 points. Now I want to make a function in which, if the data is #BAD or 0 in values for all...
Replies
0
Views
475
I have DI module ICPCon M7024UD connect to my pc using COM3 MODBUS RTU and also RHT sensors are using MODBUS TCPIP.. The problem is, it cannot...
Replies
9
Views
1,665
Since upgrading to V6.2 12.24 SP12 24-21 the M221 PLC is no longer recognised by the HMI. The screen still works but it does not talk with the...
Replies
3
Views
991
Back
Top Bottom