Hi I have an IEC motor 4pole motor 50Hz 5.5kw. It is stamped with 1540rpm. Is this even possible for a 4-pole motor?
 
The base speed on a 4 pole 50Hz motor is 1500 rpm
n = f (2 / p) 60 (1)
where
n = shaft rotation speed (rev/min, rpm)
f = frequency of electrical power supply (Hz, cycles/sec, 1/s)
p = number of poles

so it would not be possible to have run at 1540
but if it is a 60 Hz motor the base speed would 1800 rpm
1540 would be a very high slip motor if it slipped that far it would run very hot
so the numbers don't make sense
 
Not so if its a generator then for a 4 pole it would need to be driven at 1500 rom for 50HZ
and 1800 rpm for 60 HZ
The number of pols, Hz and the RPMs will still be the same weather is a motor or a generator
again the numbers as posted don't make sense it think the numbers got transposed
1540 should be 1450 that would make sense that would be about .05 % slip
or 50rpm slip under load sounds about right
 
An asynchronous induction motor if it acts as a generator will rotate at more r.pm. than the frequency revs.

If it were a synchronous generator it would spin at the exact frequency revs.

But I also think that the one who printed 1540 was wrong.
 
From the manual

60 Hz. - 1850 RPM, NL to 1800 RPM, FL
50 Hz. - 1540 RPM, NL to 1500 RPM, FL
it's a generator not a motor no load RPM 1540 for 50HZ
that 40 rpm slip from no load to full load
the frequency will be a little higher at no load
obviously not intended to line synced
 
1540rpm

Hi All,

Yes, turns out that is is a generator that shall be run as a motor. The way I see it it is a standard motot respeced.

One thing that is strange is that they specify Locked Rotor Time:
12s(hot)
22s(cold)

I have never seen this specified on a motor why would that be specified here? If running as a motor will it stay in locked rotor state for 12-22s or is that max permissible?
 
Last edited:
Guessing here, but I would assume that is the max permissible. Seems like a long time but that thing may be a tank.
 
Originally posted by Karsten:

I have never seen this specified on a motor why would that be specified here?

If you know how to do it (and I most certainly don't) you can use those two numbers to develop a thermal model of the motor/generator based on a given current through it and an assumed ambient temperature. If you know how it heats up you can figure out how it cools down as well.

Keith
 

Similar Topics

Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
128
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
331
Hello all, In my facility we have multiple 3HP 460V motors that are being controlled by VFDs which drive conveyor belts. The drives are randomly...
Replies
2
Views
200
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
Replies
18
Views
986
Kindly, has anyone tried to control Lenze servomotors with Siemens S120 drives ? Any special hints ? Have some concerns for the resolver and servo...
Replies
5
Views
228
Back
Top Bottom