hi everyone;
I have just started with panelview and communication with ML 1200 DF1 232 comport 1, I made the net configuration appear in the picture, but the rslinxs cant see the Pv and ml1200 DF1, when i set the belden cable with next configuration on pic, the firts aic doesnt blinks the RS485 but the second in there are pv550 and ml1200 rs485, minidin and df1 are blinking

the cable belden is worng or ??
because if i concect the ml1200 to port 1 and pv on port 4 i can see then on rslinx on direrent drivers.

Migul V.
Thanks in advance.

belden config.JPG PV AND ML1200.JPG
 
The network you describe is ideal for DH485 protocol but will not work with DF1 Full Duplex protocol.

Post the exact part number of your PanelView 550, and I can tell you which protocol options you have.
 
hi ,
PV CAT 2711-t5a16l1 ser. b rev. b, ok I ave to make a DH485 om ML1200 is easier but how can I switch the protocol on PV ???
the panel view has 2 rsr conectors "Rs-232 and rs232(DF1) I am connecting on DF1.
 

Similar Topics

Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
Replies
43
Views
2,836
Which signals do I have to use to get data from camera. For example camera detects a defect and sends signal to controller. Power cable: CCB-PWRIO-05
Replies
1
Views
210
can i send and recieve data using my yokogawa UT35A controller with my siemens s7 1200 plc using profinet communication without using gsd file
Replies
1
Views
381
Good day, everyone, We're trying to establish an S7 connection on ethernet between an S7-400 CPU and a new S7-1200 CPU (which is defined as slave...
Replies
10
Views
2,619
I don't have any prior experience with MicroLogix so the Communication Toggle Button is new to me. We currently have a few MicroLogix that are...
Replies
4
Views
2,208
Back
Top Bottom