So, ran across a part today that I can't really figure out where it would be used.

Its a 4 wire contactor with a NC circuit, when you power the coil it drops power from the load side. To me thats a safety type relay, but I don't see where you would want to use that on a motor. Also, it has 4 high load terminals no AUX like most AB relays.

Just looking for some knowledge because were all here scratching our heads saying why would we ever use this? :confused:
 
Maybe for a crane with electromagnet for picking up stuff ?
When the E-stop is pressed, or if there is some kind of electrical problem, the electromagnet defaults to ON. This so it does not drop a ton of steel onto some unfortunate person.
Of course the power supply for the electromagnet must still be on for this to work. I have seen this before as an example of an electrical circuit that should be exempted from the E-stop circuit.
 
Probably an old “DC drive contactor”. The NC pole was used in a braking scheme when you absolutely wanted braking every time the drive turned off, like on a hoist. Not much call for them any more, most everyone has gone to AC drives on hoists now.
 
i have seen some 4poles with 2 power no and 2 power nc terminal for forward/reverse action on a single coil.
4 NC could also be for load control system. A controler that remove heaters or other non mandatory load to limit the peak read by the utility meter. NC or mechanically held contactor are used to avoid the ''humm'' noise of holding a NO closed in some offices or quiet workplaces...
 
It is probably used or as a simple on/off contactor as the motor stops when two wires are open.
or can be used to change direction.
 
It could be as a safety relay to kill all power when activated, when the E-Stop relay shuts of it has a NC contact that would then power this contactor, which would interrupt all power.

Sort of like the N.O. solenoid valve I put on the water meter at my house - if my alarm PLC detects a flood in the basement, or I activate it by the HMI, powering the SOL on shuts off the water to the house. That way I don't have to keep the valve powered on constantly, only when I want to shut off the water.
 

Similar Topics

Hi, guys, I am confused on parameter 82, PowerFlex 70. 082 Maximum Speed: default: 50 or 60 HZ, min/max: 5.0/500.0 HZ. Now, we have a...
Replies
4
Views
5,290
Which of the following input operations require a conversion to digital form prior to input? a) disk b) analog c) contact closures d) limit...
Replies
12
Views
3,825
Hey all! I recently purchased myself a Panelview Plus off of ebay and i was hoping that i could upgrade the firmware on it to Version 9 or so and...
Replies
7
Views
2,689
Good morning everyone. I am apparently confused on the COP instruction. What I am trying to do is copy a DINT to a DINT in a User Defined Data...
Replies
16
Views
6,785
Hey guys, Im currently using the above flex IO to turn on two outputs these outputs go to two flashing red beacon lights. Here's the scenario: My...
Replies
4
Views
1,680
Back
Top Bottom